13D only requires you add it if you use the simplified calc method in 13D.

On Fri, Sep 23, 2011 at 12:06 PM, Trevor Spain <[email protected]>wrote:

> "22.4.4.7 (5) Do not include fitting loss for straight-through flow in a
> tee or cross." Seems clear to me. It doesn't say " ... unless manufacturers
> data ... ".
>
> 13D does require inclusion of loss for straight-through flow. That's why
> the information is in cpvc and pex data sheets.
>
> Trevor Spain
> Igneus Incorporated
>
>
>
> On 9/23/2011 1:55 PM, Steve Leyton wrote:
>
>> I mean to say that if you peruse the manufacturer's data sheets for
>> products like CPVC and PEX they require it in very clear language.   I
>> believe that the press-type fittings do as well.  Not in every case -
>> Jamie alluded to the fitting chart in NFPA 13 for example.
>>
>>
>> Steve Leyton
>>
>>
>>
>>
>> -----Original Message-----
>> From: 
>> sprinklerforum-bounces@**firesprinkler.org<[email protected]>
>> [mailto:sprinklerforum-**[email protected]<[email protected]>]
>> On Behalf Of Bob
>> Sent: Friday, September 23, 2011 11:45 AM
>> To: sprinklerforum@firesprinkler.**org <[email protected]>
>> Subject: RE: "flow through tee's and Hydraulic calculations"
>>
>> I either misunderstand what is being said here, or my ignorance is about
>> to
>> show through, but I have never heard anyone say that "you absolutely
>> have to
>> include" a flow through tee in calculations regardless of type.  13
>> 22.4.4.7(5) seems clear to me that you don't include this fitting
>> regardless
>> of schedule.  Am I missing something?
>>
>> Thanks,
>>
>> Bob Knight, CET III
>> 208-318-3057
>> www.firebyknight.com
>>
>>
>>
>> -----Original Message-----
>> From: 
>> sprinklerforum-bounces@**firesprinkler.org<[email protected]>
>> [mailto:sprinklerforum-**[email protected]<[email protected]>]
>> On Behalf Of Steve
>> Leyton
>> Sent: Friday, September 23, 2011 12:13 PM
>> To: sprinklerforum@firesprinkler.**org <[email protected]>
>> Subject: RE: "flow through tee's and Hydraulic calculations"
>>
>> Manufacturer's data sheets give the values and instruct on use - see
>> BlazeMaster design guide, for ex.   Yes, you absolutely have to include
>> ...
>>
>>
>> Steve Leyton
>>
>>
>>
>>
>> -----Original Message-----
>> From: 
>> sprinklerforum-bounces@**firesprinkler.org<[email protected]>
>> [mailto:sprinklerforum-**[email protected]<[email protected]>]
>> On Behalf Of Seidl
>> Jamie
>> D.
>> Sent: Friday, September 23, 2011 10:11 AM
>> To: sprinklerforum@firesprinkler.**org <[email protected]>
>> Subject: "flow through tee's and Hydraulic calcultions"
>>
>> Hello forumites, I'd like to pole the forum and see what the consensus
>> is on
>> accounting for flow through tee's or "tee on the run" when calculating a
>> system.  NFPA states that they do not need to be included when using the
>> schedule 40 fitting table.  But when using manufactures'
>> fitting equivalents, do you include them?
>>
>> -------------- next part --------------
>> An HTML attachment was scrubbed...
>> URL:
>> <http://fireball.**firesprinkler.org/mailman/**
>> private/sprinklerforum/attach<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach>
>> ments/20110923/dfa2b426/**attachment.html>
>> ______________________________**_________________
>> Sprinklerforum mailing list
>> Sprinklerforum@firesprinkler.**org <[email protected]>
>> http://fireball.firesprinkler.**org/mailman/listinfo/**sprinklerforum<http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum>
>> ______________________________**_________________
>> Sprinklerforum mailing list
>> Sprinklerforum@firesprinkler.**org <[email protected]>
>> http://fireball.firesprinkler.**org/mailman/listinfo/**sprinklerforum<http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum>
>>
>> ______________________________**_________________
>> Sprinklerforum mailing list
>> Sprinklerforum@firesprinkler.**org <[email protected]>
>> http://fireball.firesprinkler.**org/mailman/listinfo/**sprinklerforum<http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum>
>> ______________________________**_________________
>> Sprinklerforum mailing list
>> Sprinklerforum@firesprinkler.**org <[email protected]>
>> http://fireball.firesprinkler.**org/mailman/listinfo/**sprinklerforum<http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum>
>>
>>
>>  ______________________________**_________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.**org <[email protected]>
> http://fireball.firesprinkler.**org/mailman/listinfo/**sprinklerforum<http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum>
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20110923/d568ccc8/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to