Damien - I can't speak with absolute authority, but I'm pretty sure FM does not recognize the room design method. However, I THINK you may be able to get them to limit design areas when you have a room that's surrounded by rated walls. E.g. a storage room surrounded by 1-hr. walls could be designed to the room only (assuming it is under the 1,500 sq.ft. or whatever design area). I would verify with the FM Engineer on the job. Actually, having said that, you should attempt to talk to that engineer in the first place. It is ultimately their decision what they allow, and you may get one who is more sympathetic to your arguments for room design.
Mark A. Sornsin, PE| Fire Protection Engineer Ulteig Engineers, Inc.| Fargo, NDÂ [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Damien Shannon Sent: Monday, October 03, 2011 5:25 AM To: [email protected] Subject: FM Room Design type calc? Dear forum. I am unable to see anywhere in the new FM Datasheets (i.e. 2-0 &3-0 as opposed to the old 2-8N), where it allows for any type of a Room Design type calculation. Not having this allowance would seem to create havoc in certain situations. E.g. If you have a storage room (that would otherwise qualify for Room Design), next to an administrative area. Or where you have some rooms protected with EC spks next to areas with SSP/Us. Any thoughts or insight would be appreciated. Damien Shannon Director of Sales and Technical Affairs Provincial Sprinkler Company Ltd. Unit 4, Cork Airport Industrial Estate Kinsale Road, Cork, Ireland. Office: (021) 496 5058 Mobile: (086) 788 8222 Fax: (021) 431 7425 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum