Thank you for the response Mark. I didn't see anything allowing it either though as you mention the FM Engineer on a given project can make decisions such as this. Problem is if you're at bidding stage (and the client gives you a day to price it), often there isn't time to make the enquiry. Pricing for the worst case scenario will often lose the job. Also we come across projects where the specifications will state that the installation is to comply with FM 2-0 and 3-0 even though FM is not the insurer and therefore do not have a representative to query.
The only section that I see that seems to be allowing for 'room design' type calc, is section 2.1.1.10.3 of FM 3-26. However this is restricted to use of EC sprinklers in a corridor. Thanks again for your reply Mark. Damien Shannon Director of Sales and Technical Affairs Provincial Sprinkler Company Ltd. Unit 4, Cork Airport Industrial Estate Kinsale Road, Cork, Ireland. Office: (021) 496 5058 Mobile: (086) 788 8222 Fax: (021) 431 7425 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Mark Sornsin Sent: 04 October 2011 17:24 To: [email protected] Subject: RE: FM Room Design type calc? Damien - I can't speak with absolute authority, but I'm pretty sure FM does not recognize the room design method. However, I THINK you may be able to get them to limit design areas when you have a room that's surrounded by rated walls. E.g. a storage room surrounded by 1-hr. walls could be designed to the room only (assuming it is under the 1,500 sq.ft. or whatever design area). I would verify with the FM Engineer on the job. Actually, having said that, you should attempt to talk to that engineer in the first place. It is ultimately their decision what they allow, and you may get one who is more sympathetic to your arguments for room design. Mark A. Sornsin, PE| Fire Protection Engineer Ulteig Engineers, Inc.| Fargo, ND [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Damien Shannon Sent: Monday, October 03, 2011 5:25 AM To: [email protected] Subject: FM Room Design type calc? Dear forum. I am unable to see anywhere in the new FM Datasheets (i.e. 2-0 &3-0 as opposed to the old 2-8N), where it allows for any type of a Room Design type calculation. Not having this allowance would seem to create havoc in certain situations. E.g. If you have a storage room (that would otherwise qualify for Room Design), next to an administrative area. Or where you have some rooms protected with EC spks next to areas with SSP/Us. Any thoughts or insight would be appreciated. Damien Shannon Director of Sales and Technical Affairs Provincial Sprinkler Company Ltd. Unit 4, Cork Airport Industrial Estate Kinsale Road, Cork, Ireland. Office: (021) 496 5058 Mobile: (086) 788 8222 Fax: (021) 431 7425 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum