On a current government project, piping has been hung from a concrete
filled metal deck using expansion shells (drop-in). After giving the
okay to use this type of hanger, an inspector has referenced :
"9.2.1.4.1 Metal Deck. 9.2.1.4.1 * Branch line hangers attached to
metal deck shall be permitted only for the support of pipe 1 in. (25
mm) or smaller in size, by drilling or punching the vertical portion
of the metal deck and using through bolts." and in Annex A, it says
that "A.9.2.1.4.1 The requirements of 9.2.1.4.1 are based on metal
decks only but can be applied to other applications such as concrete
or gypsum-filled metal decks".

In 9.1.3 Fasteners in Concrete, it notes that "Unless prohibited by
9.1.3.2 or 9.1.3.3, the use of listed inserts set in concrete and
listed post-installed anchors to support hangers shall be permitted
for mains and branch lines.
9.1.3.2 Post-installed anchors shall not be used in cinder concrete,
except for branch lines where the post-installed anchors are
alternated with through-bolts or hangers attached to beams.
9.1.3.3 Post-installed anchors shall not be used in ceilings of gypsum
or other similar soft material.

The expansion shells are in the concrete portion of the deck (the
metal decking has been drilled to permit the expansion shells to be
inserted into the concrete). Doesn't this comply with 9.1.3 ?

Daniel N. Adams
Designer

Interwest Fire Protection, Inc.