It is 4" total thickness on 1" non-composite metal deck.

On Mon, Nov 21, 2011 at 1:50 PM, Matt Grise <[email protected]> wrote:
> How thick is the concrete?
>
> Matt Grisé PE*, LEED AP
> Sales Engineer
> Alliance Fire Protection
> 130 w 9th Ave.
> North Kansas City, MO 64116
>
> *Licensed in KS & MO
>
> 913.888.0647 ph
> 913.888.0618 f
> 913.927.0222 cell
> www. AFPsprink.com
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Daniel Adams
> Sent: Monday, November 21, 2011 2:48 PM
> To: [email protected]
> Subject: Hanger question (NFPA 13, 2007 edition)
>
> On a current government project, piping has been hung from a concrete
> filled metal deck using expansion shells (drop-in). After giving the
> okay to use this type of hanger, an inspector has referenced :
> "9.2.1.4.1 Metal Deck. 9.2.1.4.1 * Branch line hangers attached to
> metal deck shall be permitted only for the support of pipe 1 in. (25
> mm) or smaller in size, by drilling or punching the vertical portion
> of the metal deck and using through bolts." and in Annex A, it says
> that "A.9.2.1.4.1 The requirements of 9.2.1.4.1 are based on metal
> decks only but can be applied to other applications such as concrete
> or gypsum-filled metal decks".
>
> In 9.1.3 Fasteners in Concrete, it notes that "Unless prohibited by
> 9.1.3.2 or 9.1.3.3, the use of listed inserts set in concrete and
> listed post-installed anchors to support hangers shall be permitted
> for mains and branch lines.
> 9.1.3.2 Post-installed anchors shall not be used in cinder concrete,
> except for branch lines where the post-installed anchors are
> alternated with through-bolts or hangers attached to beams.
> 9.1.3.3 Post-installed anchors shall not be used in ceilings of gypsum
> or other similar soft material.
>
> The expansion shells are in the concrete portion of the deck (the
> metal decking has been drilled to permit the expansion shells to be
> inserted into the concrete). Doesn't this comply with 9.1.3 ?
>
> Daniel N. Adams
> Designer
>
> Interwest Fire Protection, Inc.
> 404 Ironwood Drive
> Salt Lake City, UT 84115
>
> Phone:     (801) 746-4040
> Fax:         (801) 746-4043
> [email protected]
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum



-- 
Daniel N. Adams
Designer

Interwest Fire Protection, Inc.
404 Ironwood Drive
Salt Lake City, UT 84115

Phone:     (801) 746-4040
Fax:         (801) 746-4043
[email protected]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to