You're welcome, and that last sentence should have read "built up" not build 
up.  Whatever.

SL




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Daniel Adams
Sent: Monday, November 21, 2011 1:22 PM
To: [email protected]
Subject: Re: Hanger question (NFPA 13, 2007 edition)

Thanks Steve, I appreciate your insight !

On Mon, Nov 21, 2011 at 2:16 PM, Steve Leyton
<[email protected]> wrote:
> It's not a metal deck, it's a poured-in-place-concrete-reinforced metal deck. 
>  The cited section is for attaching to unreinforced metal deck such as roof 
> decks with nothing more than insulation or build up composition roof on top.
>
> Steve L.
>
>
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Daniel Adams
> Sent: Monday, November 21, 2011 1:14 PM
> To: [email protected]
> Subject: Re: Hanger question (NFPA 13, 2007 edition)
>
> It is 4" total thickness on 1" non-composite metal deck.
>
> On Mon, Nov 21, 2011 at 1:50 PM, Matt Grise <[email protected]> wrote:
>> How thick is the concrete?
>>
>> Matt Grisé PE*, LEED AP
>> Sales Engineer
>> Alliance Fire Protection
>> 130 w 9th Ave.
>> North Kansas City, MO 64116
>>
>> *Licensed in KS & MO
>>
>> 913.888.0647 ph
>> 913.888.0618 f
>> 913.927.0222 cell
>> www. AFPsprink.com
>>
>>
>> -----Original Message-----
>> From: [email protected] 
>> [mailto:[email protected]] On Behalf Of Daniel Adams
>> Sent: Monday, November 21, 2011 2:48 PM
>> To: [email protected]
>> Subject: Hanger question (NFPA 13, 2007 edition)
>>
>> On a current government project, piping has been hung from a concrete
>> filled metal deck using expansion shells (drop-in). After giving the
>> okay to use this type of hanger, an inspector has referenced :
>> "9.2.1.4.1 Metal Deck. 9.2.1.4.1 * Branch line hangers attached to
>> metal deck shall be permitted only for the support of pipe 1 in. (25
>> mm) or smaller in size, by drilling or punching the vertical portion
>> of the metal deck and using through bolts." and in Annex A, it says
>> that "A.9.2.1.4.1 The requirements of 9.2.1.4.1 are based on metal
>> decks only but can be applied to other applications such as concrete
>> or gypsum-filled metal decks".
>>
>> In 9.1.3 Fasteners in Concrete, it notes that "Unless prohibited by
>> 9.1.3.2 or 9.1.3.3, the use of listed inserts set in concrete and
>> listed post-installed anchors to support hangers shall be permitted
>> for mains and branch lines.
>> 9.1.3.2 Post-installed anchors shall not be used in cinder concrete,
>> except for branch lines where the post-installed anchors are
>> alternated with through-bolts or hangers attached to beams.
>> 9.1.3.3 Post-installed anchors shall not be used in ceilings of gypsum
>> or other similar soft material.
>>
>> The expansion shells are in the concrete portion of the deck (the
>> metal decking has been drilled to permit the expansion shells to be
>> inserted into the concrete). Doesn't this comply with 9.1.3 ?
>>
>> Daniel N. Adams
>> Designer
>>
>> Interwest Fire Protection, Inc.
>> 404 Ironwood Drive
>> Salt Lake City, UT 84115
>>
>> Phone:     (801) 746-4040
>> Fax:         (801) 746-4043
>> [email protected]
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
>
> --
> Daniel N. Adams
> Designer
>
> Interwest Fire Protection, Inc.
> 404 Ironwood Drive
> Salt Lake City, UT 84115
>
> Phone:     (801) 746-4040
> Fax:         (801) 746-4043
> [email protected]
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum



-- 
Daniel N. Adams
Designer

Interwest Fire Protection, Inc.
404 Ironwood Drive
Salt Lake City, UT 84115

Phone:     (801) 746-4040
Fax:         (801) 746-4043
[email protected]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to