Mike:

The old Model B deluge valve cannot hold air pressure without a riser check 
valve installed above it.  The alarm line trim is directly connected to the 
inside of the deluge valve without the use of any intermediate type chamber in 
the seat.  Therefore, air pressure introduced into the valve will leak directly 
out the automatic ball drip valve on the alarm line. This design permits visual 
inspection at the ball drip for any leaks at the seat, as well as enabling 
draining of any water due to condensation or drainback.  By installing a valve 
on this line, you lose visually a way to detect a leak at the seat, as well as 
prevent a waterflow alarm occurring from the eventual buildup of pressure from 
such leak.
.

Salvatore J. Izzo, P.E. SFPE,  Manager - Technical Services
The Reliable Automatic Sprinkler Company, Inc.
103 Fairview Park Dr.
Elmsford, NY  10523
Tel:  (864) 843-5252     Fax:  (864) 843-3073
E-mail:  [email protected]
________________________________________
From: [email protected] 
[[email protected]] On Behalf Of Morey, Mike 
[[email protected]]
Sent: Thursday, December 01, 2011 1:40 PM
To: [email protected]
Subject: Reliable Model B Deluge Valve - Air Supervision

We have what amounts to a closed head electronically actuated deluge system, or 
maybe a non interlock electronically actuated preaction system?  I'm not even 
sure how to make the distinction.  It utilizes a reliable model B 6" deluge 
valve that appears to have more or less standard trim and an alarm pressure 
switch.  We're attempting to convert the system to low pressure nitrogen 
supervision only to monitor the integrity of the pipe.  The issue we're running 
into is that when we attempt to pressurize the system the ball drip/velocity 
check in the alarm pressure switch trim leaks air at a high rate.  The proposal 
was to add a check valve above the deluge valve to allow an intermediate 
chamber without air pressure to be monitored for alarms, but this adds another 
drain, pressure gauge etc that will all have to be piped into 2 large and 
unwieldy systems that are already installed.  Is there anything that would 
prohibit us from just replacing the ball drip valve with a standard d
 rain valve, or adding a shutoff in front of the ball drip?  These systems are 
pretty meticulously maintained so draining off the alarm line wouldn't be a 
major issue.  Code wise I can't see anything that mandates the presence of the 
valve, it seems to be more to allow condensate to drain and allow the alarm 
line to be drained quickly after a trip.

Mike Morey, SET, CFPS
Sprinkler Designer
BMW Constructors, Inc.
O: 317.651.0596 | C: 317.586.8111
www.bmwc.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111201/cac144ef/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to