Two point to be made. This section is limited to just the 3 methods as part of methodologies for just spray sprinklers. As such it's past the time that this section should be deleted. I say this because a more comprehensive statement is in 11.1.1. If you go there, you'll notice it says "A building OR PORTION THEREOF" can use any applicable design basis. As such, mentally add to 11.2.3.1.1 that you can use only one method within the portion of the building for which it is being applied. Before someone asks - You can have many design basis within a single system.

Apply NFPA caveat that this is my option as a technical member and not that of NFPA.

Roland


On Dec 7, 2011, at 5:59 AM, Cory Power wrote:

Reading the following from NFPA 13 2010 ed. Does this mean the room design method cannot be used in an area if we already used the density/area method in another area? We have a residence with a mechanical penthouse using the density/area method but the floors below are all residential units separated by block walls. Are we be allowed to use room design method for that?


11.2.3.1.1 The water supply for sprinklers shall be determined
*only from one* of the following, at the discretion of the
designer:
(1) Density/area curves of Figure 11.2.3.1.1 in accordance
with the density/area method of 11.2.3.2
(2) The room that creates the greatest demand in accordance
with the room design method of 11.2.3.3
(3) Special design areas in accordance with 11.2.3.4
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111207/55489866/attachment.html >
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to