You're pushing this Jack. Your first remote area does not refer to
sprinkler systems at all and the second is just grids. I'll give you a
punchy on one and a point kinda made on two.


On Wed, Dec 7, 2011 at 11:32 AM, Justin Reid
<[email protected]>wrote:

> You need to put "hydraulically" in front of remote to look at the intent.
> It has been shortened to be called the remote area but the intent is to be
> the hydraulically remote area.
>
> Justin Reid
>
> On Wed, Dec 7, 2011 at 1:47 PM, Fairchild, Jack <
> [email protected]
> > wrote:
>
> > That was last month's discussion, but since I'm feeling particularly
> > punchy...  I'll agree to drop the term "remote area" when NFPA 13 does.
> >  What's really funny is that NFPA 13 uses it both ways!
> >
> > 8.17.2.2
> > (1) Buildings located in remote areas that are inaccessible for fire
> > department support.
> > and
> > 22.3.3
> > (15)* Diagram to accompany gridded system calculations to indicate flow
> > quantities and directions for lines with sprinklers operating in the
> remote
> > area.
> >
> >
> > Jack Fairchild
> >
> > -----Original Message-----
> > From: [email protected] [mailto:
> > [email protected]] On Behalf Of Ron Greenman
> > Sent: Wednesday, December 07, 2011 10:30 AM
> > To: [email protected]
> > Subject: Re: Multiple design methods in one building
> >
> > I really wish we'd just drop the term "remote area" as it only applies
> when
> > the the hydraulically most demanding area is actually also the most
> remote.
> > I know what you mean but lots of folks out there really think the terms
> > are synonymous.
> >
> > On Wed, Dec 7, 2011 at 6:38 AM, Fairchild, Jack <
> > [email protected]
> > > wrote:
> >
> > > I believe you are saying:  Calculate the most remote area using the
> > > appropriate method.
> > > For example:  A 1500 sq.ft. remote area in a corridor will probably be
> > > more demanding that a corridor calculation, but because it is not an
> > > appropriate method you don't do it.
> > >
> > > Jack Fairchild
> > >
> > >
> > > -----Original Message-----
> > > From: [email protected] [mailto:
> > > [email protected]] On Behalf Of
> > > [email protected]
> > > Sent: Wednesday, December 07, 2011 9:26 AM
> > > To: [email protected]
> > > Subject: RE: Multiple design methods in one building
> > >
> > > I am referring to the methods of determining a light hazard remote
> area.
> > > Room design, area density and corridor are the ones I remember. Each
> > method
> > > is allowed and each will result in a different flow requirement. There
> is
> > > no requirement to design the sprinkler system to the most demanding.
> > >
> > >
> > > Ron Fletcher
> > > Aero Automatic
> > > Phoenix, AZ
> > >
> > >
> > >
> > >
> > > -----Original Message-----
> > > From: [email protected] [mailto:
> > > [email protected]] On Behalf Of Fairchild, Jack
> > > Sent: Wednesday, December 07, 2011 6:59 AM
> > > To: [email protected]
> > > Subject: RE: Multiple design methods in one building
> > >
> > > Ron,
> > >
> > > Please clarify your statement.  Which "methods" are your referring to?
> > >  Are you talking about Hazen-Williams vs. Darcy-Weisbach?
> > >
> > >
> > > Jack Fairchild
> > >
> > > -----Original Message-----
> > > From: [email protected] [mailto:
> > > [email protected]] On Behalf Of
> > > [email protected]
> > > Sent: Wednesday, December 07, 2011 8:45 AM
> > > To: [email protected]
> > > Subject: RE: Multiple design methods in one building
> > >
> > > It also supports "not" requiring that the method resulting in the
> > greatest
> > > demand be used. In LH there are many methods of determining the remote
> > area
> > > but no requirement that the most demanding method be used.
> > >
> > >
> > > Ron Fletcher
> > > Aero Automatic
> > > Phoenix, AZ
> > >
> > >
> > >
> > > -----Original Message-----
> > > From: [email protected] [mailto:
> > > [email protected]] On Behalf Of Todd Williams
> > > Sent: Wednesday, December 07, 2011 5:15 AM
> > > To: [email protected]
> > > Subject: Re: Multiple design methods in one building
> > >
> > > In the Handbook commentary, it states "It is possible for a combination
> > of
> > > design methods to be used in a single building". I perceive the purpose
> > of
> > > this section is to make it the designer's discretion on which approach
> to
> > > use, so an authority cannot mandate something different after the fact
> > > (unless specifically included as part of a job specification). I think
> > you
> > > are good mixing it up.
> > >
> > >
> > > At 06:59 AM 12/7/2011, you wrote:
> > > >Reading the following from NFPA 13 2010 ed.  Does this mean the room
> > > design method cannot be used in an area if we already used the
> > density/area
> > > method in another area? We have a residence with a mechanical penthouse
> > > using the density/area method but the floors below are all residential
> > > units separated by block walls. Are we be allowed to use room design
> > method
> > > for that?
> > > >
> > > >
> > > >11.2.3.1.1 The water supply for sprinklers shall be determined
> > > >*only from one* of the following, at the discretion of the
> > > >designer:
> > > >(1) Density/area curves of Figure 11.2.3.1.1 in accordance
> > > >with the density/area method of 11.2.3.2
> > > >(2) The room that creates the greatest demand in accordance
> > > >with the room design method of 11.2.3.3
> > > >(3) Special design areas in accordance with 11.2.3.4
> > > >-------------- next part --------------
> > > >An HTML attachment was scrubbed...
> > > >URL: <
> > >
> >
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111207/55489866/attachment.html
> > > >
> > > >_______________________________________________
> > > >Sprinklerforum mailing list
> > > >[email protected]
> > > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > > Todd G. Williams, PE
> > > Fire Protection Design/Consulting
> > > Stonington, CT
> > > 860.535.2080
> > > www.fpdc.com
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> >
> >
> >
> > --
> > Ron Greenman
> > Instructor
> > Fire Protection Engineering Technology
> > Bates Technical College
> > 1101 So. Yakima Ave.
> > Tacoma, WA 98405
> >
> > [email protected]
> >
> > http://www.bates.ctc.edu/fireprotection/
> >
> > 253.680.7346
> > 253.576.9700 (cell)
> >
> > Member:
> > ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC
> >
> > They are happy men whose natures sort with their vocations. -Francis
> Bacon,
> > essayist, philosopher, and statesman (1561-1626)
> > -------------- next part --------------
> > An HTML attachment was scrubbed...
> > URL: <
> >
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111207/ea5fee97/attachment.html
> > >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111207/77503b98/attachment.html
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111207/b524fa58/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to