Commonly misunderstood and misapplied. The intent of hose stream allowance is to margin at the water supply, not at the BOR or common supply point of a combined system. HSA at the city connection for a sprinkler calc, FDC inlets as source node for your manual standpipe calc'.
Just me, not the TC, Steve L. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Dewayne Martinez Sent: Wednesday, December 21, 2011 1:37 PM To: SprinklerFORUM Subject: Manual-wet standpipe hose demand Do I need to include the hose allowance for a manual-wet standpipe in calc for the LH system at the base of riser or do I just add 100GPM at the road? Thanks, Dewayne Martinez Design Build Fire Protection 262-781-7900 (w) 262-781-8401 (f) 414-349-0468 (cell) -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach ments/20111221/affa1a78/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum