When you have small hose connections per 8.17.5.   Note that 8.17.5.1.2
specifically disclaims that small hose connections are required to meet
the requirements of a standpipe system.

SML




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Wednesday, December 21, 2011 2:07 PM
To: [email protected]
Subject: RE: Manual-wet standpipe hose demand

Thanks Steve,  so when does 11.1.6.5 (NFPA 13,2010ed) come into play?
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve
Leyton
Sent: Wednesday, December 21, 2011 3:58 PM
To: [email protected]
Subject: RE: Manual-wet standpipe hose demand

Commonly misunderstood and misapplied.   The intent of hose stream
allowance is to margin at the water supply, not at the BOR or common
supply point of a combined system.  HSA at the city connection for a
sprinkler calc, FDC inlets as source node for your manual standpipe
calc'.

Just me, not the TC,

Steve L.




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Wednesday, December 21, 2011 1:37 PM
To: SprinklerFORUM
Subject: Manual-wet standpipe hose demand

Do I need to include the hose allowance for a manual-wet standpipe in
calc for the LH system at the base of riser or do I just add 100GPM at
the road?

 

Thanks,

Dewayne Martinez

Design Build Fire Protection

262-781-7900 (w)

262-781-8401 (f)

414-349-0468 (cell)

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20111221/affa1a78/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to