To those in urban seismic areas:

When required to provide the onsite secondary water supply, is the pump/tank 
required to provide 100 psi at the top of a combination standpipe or just 
sprinkler pressure demand?  I have a situation where the city/pump combination 
can meet the standpipe pressure demands at the top, but the tank/pump doesn't.


I have two projects with new high rise buildings being constructed.  Both are 
campus style pumping arrangements (no underground pipe).  One of the projects 
has an existing pump/tank combination which was not designed to meet 100 psi at 
the top based on tank alone.  The combination pump/city supply does meet the 
standpipe pressure demand, but not the pump/tank.

The other project has a pump/city supply which I am adding a pump/tank to.  The 
new pump is redundancy only.  Adding the tank without increasing the pump size 
will not provide 100 psi at the top.


[F] 903.3.5.2 Secondary water supply. A secondary on-site water supply equal to 
the hydraulically calculated sprinkler demand, including the hose stream 
requirement, shall be provided for high-rise buildings assigned to Seismic 
Design Category C, D, E or F as determined by this code. The secondary water 
supply shall have a duration of not less than 30 minutes as determined by the 
occupancy hazard classification in accordance with NFPA 13. 

Exception: Existing buildings.


Jack Fairchild