I Think you've answered your own question.  "The secondary water supply shall 
have a duration of not less than 30 minutes as determined by the occupancy 
hazard classification in accordance with NFPA 13."
13 doesn't specify standpipe demands.  The one I've done in the past was only 
required to maintain sprinkler durations, not standpipe operations. 

Jamie Seidl

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Fairchild, Jack
Sent: Thursday, December 22, 2011 8:39 AM
To: [email protected]
Subject: Pressure Requirements for Secondary Onsite Water Supply

To those in urban seismic areas:

When required to provide the onsite secondary water supply, is the pump/tank 
required to provide 100 psi at the top of a combination standpipe or just 
sprinkler pressure demand?  I have a situation where the city/pump combination 
can meet the standpipe pressure demands at the top, but the tank/pump doesn't.


I have two projects with new high rise buildings being constructed.  Both are 
campus style pumping arrangements (no underground pipe).  One of the projects 
has an existing pump/tank combination which was not designed to meet 100 psi at 
the top based on tank alone.  The combination pump/city supply does meet the 
standpipe pressure demand, but not the pump/tank.

The other project has a pump/city supply which I am adding a pump/tank to.  The 
new pump is redundancy only.  Adding the tank without increasing the pump size 
will not provide 100 psi at the top.


[F] 903.3.5.2 Secondary water supply. A secondary on-site water supply equal to 
the hydraulically calculated sprinkler demand, including the hose stream 
requirement, shall be provided for high-rise buildings assigned to Seismic 
Design Category C, D, E or F as determined by this code. The secondary water 
supply shall have a duration of not less than 30 minutes as determined by the 
occupancy hazard classification in accordance with NFPA 13. 

Exception: Existing buildings.


Jack Fairchild
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to