Jack:

As others have said, the tank is to be sized for the flow and duration
of the greatest sprinkler demand, but I want to speak to your question
about the pump.   I would also suggest you consider using a break tank.


If this is a high-rise (I assume it is, as that's where the ICC tank
provision kicks in), then you have to have an automatic standpipe system
and the 100psi is a minimum remote outlet performance criterion.  If you
size a fire pump that takes positive suction head from the city main,
you will have a higher discharge pressure and can use a smaller pump
than if your calc's utilized just the NPSH from the tank.  But if the
primary water supply is interrupted, then the pump will be producing
less total head - not a problem for the standpipes because that's not
the intent of the tank, but a problem for sprinkler demand if you used
the higher suction pressure from city supply.   Arguably, this is what
the FDC is for, but you have an on-paper discrepancy that's not very
well addressed in the code and standards.

A break tank allows you to have a steady state discharge pressure that
will vary only with the height of the water column in the tank.  It will
be more expensive because of the fill mechanisms required (redundancy
required) and the nominally larger pump, but IMHO it's a better setup.
Your discharge pressure will be one curve and you can design sprinklers
and standpipes to that performance without having to diddle around with
high/low static variations.    Keep in mind that IBC 403.3.2 requires
two city connections to pumps serving high-rise buildings; these can be
headed off at the fill lines for the tank.  


Steve Leyton 




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Fairchild, Jack
Sent: Thursday, December 22, 2011 5:39 AM
To: [email protected]
Subject: Pressure Requirements for Secondary Onsite Water Supply

To those in urban seismic areas:

When required to provide the onsite secondary water supply, is the
pump/tank required to provide 100 psi at the top of a combination
standpipe or just sprinkler pressure demand?  I have a situation where
the city/pump combination can meet the standpipe pressure demands at the
top, but the tank/pump doesn't.


I have two projects with new high rise buildings being constructed.
Both are campus style pumping arrangements (no underground pipe).  One
of the projects has an existing pump/tank combination which was not
designed to meet 100 psi at the top based on tank alone.  The
combination pump/city supply does meet the standpipe pressure demand,
but not the pump/tank.

The other project has a pump/city supply which I am adding a pump/tank
to.  The new pump is redundancy only.  Adding the tank without
increasing the pump size will not provide 100 psi at the top.


[F] 903.3.5.2 Secondary water supply. A secondary on-site water supply
equal to the hydraulically calculated sprinkler demand, including the
hose stream requirement, shall be provided for high-rise buildings
assigned to Seismic Design Category C, D, E or F as determined by this
code. The secondary water supply shall have a duration of not less than
30 minutes as determined by the occupancy hazard classification in
accordance with NFPA 13. 

Exception: Existing buildings.


Jack Fairchild
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to