Emphasis in CAPS;

2009 IBC

201.1 Scope. Unless otherwise expressly stated, the following words and
terms shall, FOR THE PURPOSES OF THIS CODE, have the meanings shown in this
chapter.

Continuing on.................

[F] 903.2.8 Group R. An automatic sprinkler system INSTALLED IN ACCORDANCE
with Section 903.3 shall be provided THROUGHOUT ALL BUILDINGS WITH A GROUP R
FIRE AREA.

[F] 903.3.1 Standards. Sprinkler systems SHALL BE DESIGNED AND INSTALLED in
accordance with Section 903.3.1.1, 903.3.1.2 or 903.3.1.3.

[F] 903.3.1.1 NFPA 13 sprinkler systems. WHERE THE PROVISIONS OF THIS CODE
REQUIRE THAT A BUILDING OR PORTION THEREOF be equipped throughout with an
automatic sprinkler
system in accordance with this section, sprinklers shall be installed
throughout IN ACCORDANCE with NFPA 13 EXCEPT AS PROVIDED in Section
903.3.1.1.1.

[F] 903.3.1.2 NFPA 13R sprinkler systems. Where allowed in buildings of
Group R, up to and including four stories in height, automatic sprinkler
systems shall be installed throughout IN ACCORDANCE WITH NFPA 13R.

[F] 903.3.1.2.1 Balconies and decks. Sprinkler protection shall be provided
for exterior balconies, decks and ground floor patios of dwelling units
where the building is of Type V construction, provided there is a roof or
deck above. Sidewall sprinklers that are used to protect such areas shall be
permitted to be located such that their deflectors are within 1 inch (25 mm)
to 6 inches (152 mm) below the structural members and a maximum distance of
14 inches (356 mm) below the deck of the exterior balconies and decks that
are constructed of open wood joist construction.

Hope that helps,

John Drucker, CET
Fire Protection Subcode Official 
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ

Not the official position of any agency, association, committee or
otherwise.  Obtain required applications, permits, inspections and approvals
from Authority(s) Having Jurisdiction. 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of David
Blackwell
Sent: Thursday, December 29, 2011 12:31 PM
To: [email protected]
Subject: RE: Dwelling Unit- 13 vrs IBC defs

Don't confuse yourself by using terms defined in one code or standard and
applying that to another.
The term is normally only good for that code or standard and are separate.
Use the IBC definition when applying IBC rules and NFPA 13 definition when
applying NFPA 13.

I can go into detail/legal if you like but this brief explanation keeps it
simple and to the point...

[If I am wrong or missed something, someone will surely speak up (knowing
the "forumites" who regularly post).]


Respectfully,


David W. S. Blackwell, II, PE, CFPE, CFI I
Chief Engineer
Office of State Fire Marshal
SC Department of Labor, Licensing, & Regulation, 141 Monticello Trail,
Columbia, SC 29203
Telephone: 803.896.9800 [Office] 803.896.9833 [Direct]
Fax: 803.896.9806 [Office]
Email:   [email protected]
Website:  http://www.scfiremarshal.llronline.com/


Please note that you can sign up to receive automatic information on SC
Division of Fire and Life Safety current events, policies, laws and
procedures by visiting our Web site at: 
http://www.scfiremarshal.llronline.com/


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Thursday, December 29, 2011 10:17 AM
To: [email protected]
Subject: Dwelling Unit- 13 vrs IBC defs

NFPA 13-'07 defines a dwelling unit in 3.3.7 and specifically calls out "For
purposes of this standard, dwelling unit includes hotel rooms,..." and there
is no requirement for cooking facilities.

2009 IBC in 202, Definitions, Dwelling Unit. A single unit providing
complete, independent living facilities for one or more persons, including
permanent provisions for living, sleeping, eating, cooking and sanitation." 

So while the installation standard clearly states hotel rooms are intended
to be protected as dwelling units, it seems that in order to qualify as
dwelling units under the IBC, permanent cooking facilities must be present,
and building codes trump installation standards. 

So does this mean when designing a system under #13 in a jurisdiction that
adopted the IBC, we can't use dwelling unit rules from 13 in a hotel if the
rooms don't contain a kitchen and bathroom?
]
It may get cloudy when the IBC continues on to require QR or Residential
sprinklers in Group R and I-1 dwelling units and sleeping units in 903.3.2
(2). 


George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Johnson,
Duane (NIH/OD/ORS) [C]
Sent: Thursday, December 29, 2011 10:00 AM
To: [email protected]
Subject: RE: NFPA 25 standpipe test

It's a holiday week...all references below are from NFPA 25.

-----Original Message-----
From: Johnson, Duane (NIH/OD/ORS) [C] 
Sent: Thursday, December 29, 2011 9:54 AM
To: [email protected]
Subject: RE: NFPA 25 standpipe test

...that is 1998 edition of NFPA 25. sorry

-----Original Message-----
From: Johnson, Duane (NIH/OD/ORS) [C] 
Sent: Thursday, December 29, 2011 9:50 AM
To: [email protected]
Subject: RE: NFPA 25 standpipe test

You must flow the system demand at time of design (14:6.3.1.3 2008 ed). The
flow test must occur at the hyd most remote outlets (14:6.3.1.2).  You only
need to do one flow test per zone (14:6.3.1.1). Your two sections do not
necessarily mean two zones.

Note also, if this is for Joint Commission, you will need to go back to the
old codes.  To my knowledge, they are enforcing NFPA 101 2000 edition...this
means the 1998 edition of NFPA 14 is applicable.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor) Office of Research
Services National Institutes of Health
301-496-0487

"Protecting Science - One Sprinkler at a Time"

-----Original Message-----
From: Todd Williams [mailto:[email protected]]
Sent: Thursday, December 29, 2011 9:15 AM
To: [email protected]
Subject: NFPA 25 standpipe test

I am working with a hospital with a total of 9 standpipes. There are
standpipes that are both pre and post 1993. The original building is
partially sprinklered and the new section is fully sprinklered. 

1. Is the intent of NFPA 25 that multiple standpipes be flowed
simultaneously to meet the 1250 gpm demand?

2. Should the two sections of the hospital be flow independent of each
other? 

3. If yes to 1 and 2, could the new section be flowed as a fully sprinklered
building (thus 1000 gpm) as opposed to 1250?

4. How should i handle pipe schedule standpipes, if any exist?

I haven't had to deal with 5 year standpipe tests before.

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to