NFPA 13-'07 defines a dwelling unit in 3.3.7 and specifically calls out "For purposes of this standard, dwelling unit includes hotel rooms,..." and there is no requirement for cooking facilities.
2009 IBC in 202, Definitions, Dwelling Unit. A single unit providing complete, independent living facilities for one or more persons, including permanent provisions for living, sleeping, eating, cooking and sanitation." So while the installation standard clearly states hotel rooms are intended to be protected as dwelling units, it seems that in order to qualify as dwelling units under the IBC, permanent cooking facilities must be present, and building codes trump installation standards. So does this mean when designing a system under #13 in a jurisdiction that adopted the IBC, we can't use dwelling unit rules from 13 in a hotel if the rooms don't contain a kitchen and bathroom? ] It may get cloudy when the IBC continues on to require QR or Residential sprinklers in Group R and I-1 dwelling units and sleeping units in 903.3.2 (2). George L. Church, Jr., CET Rowe Sprinkler Systems, Inc. PO Box 407, Middleburg, PA 17842 877-324-ROWE 570-837-6335 fax [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Johnson, Duane (NIH/OD/ORS) [C] Sent: Thursday, December 29, 2011 10:00 AM To: [email protected] Subject: RE: NFPA 25 standpipe test It's a holiday week...all references below are from NFPA 25. -----Original Message----- From: Johnson, Duane (NIH/OD/ORS) [C] Sent: Thursday, December 29, 2011 9:54 AM To: [email protected] Subject: RE: NFPA 25 standpipe test ...that is 1998 edition of NFPA 25. sorry -----Original Message----- From: Johnson, Duane (NIH/OD/ORS) [C] Sent: Thursday, December 29, 2011 9:50 AM To: [email protected] Subject: RE: NFPA 25 standpipe test You must flow the system demand at time of design (14:6.3.1.3 2008 ed). The flow test must occur at the hyd most remote outlets (14:6.3.1.2). You only need to do one flow test per zone (14:6.3.1.1). Your two sections do not necessarily mean two zones. Note also, if this is for Joint Commission, you will need to go back to the old codes. To my knowledge, they are enforcing NFPA 101 2000 edition...this means the 1998 edition of NFPA 14 is applicable. Duane Johnson, PE Program Manager Division of the Fire Marshal (Support Contractor) Office of Research Services National Institutes of Health 301-496-0487 "Protecting Science - One Sprinkler at a Time" -----Original Message----- From: Todd Williams [mailto:[email protected]] Sent: Thursday, December 29, 2011 9:15 AM To: [email protected] Subject: NFPA 25 standpipe test I am working with a hospital with a total of 9 standpipes. There are standpipes that are both pre and post 1993. The original building is partially sprinklered and the new section is fully sprinklered. 1. Is the intent of NFPA 25 that multiple standpipes be flowed simultaneously to meet the 1250 gpm demand? 2. Should the two sections of the hospital be flow independent of each other? 3. If yes to 1 and 2, could the new section be flowed as a fully sprinklered building (thus 1000 gpm) as opposed to 1250? 4. How should i handle pipe schedule standpipes, if any exist? I haven't had to deal with 5 year standpipe tests before. Todd G. Williams, PE Fire Protection Design/Consulting Stonington, CT 860.535.2080 www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum