If it were Thanksgiving I'd be thankful for East Coast guys that answer
George's questions before I get out of bed.

On Thu, Dec 29, 2011 at 11:28 AM, George Church <[email protected]>wrote:

> It's like reading the directions, isn't it?
> FOR PURPOSES OF THIS CODE....
> FOR PURPOSES OF THIS STANDARD......
>
> As always, Thanks David and John.
> Now I've got something I can work with, and its even familiar and
> comfortable.
>
> George L.  Church, Jr., CET
> Rowe Sprinkler Systems, Inc.
> PO Box 407, Middleburg, PA 17842
> 877-324-ROWE       570-837-6335 fax
> [email protected]
>
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of John Drucker
> Sent: Thursday, December 29, 2011 12:58 PM
> To: [email protected]
> Subject: RE: Dwelling Unit- 13 vrs IBC defs
>
> Emphasis in CAPS;
>
> 2009 IBC
>
> 201.1 Scope. Unless otherwise expressly stated, the following words and
> terms shall, FOR THE PURPOSES OF THIS CODE, have the meanings shown in this
> chapter.
>
> Continuing on.................
>
> [F] 903.2.8 Group R. An automatic sprinkler system INSTALLED IN ACCORDANCE
> with Section 903.3 shall be provided THROUGHOUT ALL BUILDINGS WITH A GROUP
> R FIRE AREA.
>
> [F] 903.3.1 Standards. Sprinkler systems SHALL BE DESIGNED AND INSTALLED
> in accordance with Section 903.3.1.1, 903.3.1.2 or 903.3.1.3.
>
> [F] 903.3.1.1 NFPA 13 sprinkler systems. WHERE THE PROVISIONS OF THIS CODE
> REQUIRE THAT A BUILDING OR PORTION THEREOF be equipped throughout with an
> automatic sprinkler system in accordance with this section, sprinklers
> shall be installed throughout IN ACCORDANCE with NFPA 13 EXCEPT AS PROVIDED
> in Section 903.3.1.1.1.
>
> [F] 903.3.1.2 NFPA 13R sprinkler systems. Where allowed in buildings of
> Group R, up to and including four stories in height, automatic sprinkler
> systems shall be installed throughout IN ACCORDANCE WITH NFPA 13R.
>
> [F] 903.3.1.2.1 Balconies and decks. Sprinkler protection shall be
> provided for exterior balconies, decks and ground floor patios of dwelling
> units where the building is of Type V construction, provided there is a
> roof or deck above. Sidewall sprinklers that are used to protect such areas
> shall be permitted to be located such that their deflectors are within 1
> inch (25 mm) to 6 inches (152 mm) below the structural members and a
> maximum distance of
> 14 inches (356 mm) below the deck of the exterior balconies and decks that
> are constructed of open wood joist construction.
>
> Hope that helps,
>
> John Drucker, CET
> Fire Protection Subcode Official
> Fire/Building/Electrical Inspector
> Fire Marshals Office
> Borough of Red Bank, NJ
>
> Not the official position of any agency, association, committee or
> otherwise.  Obtain required applications, permits, inspections and
> approvals from Authority(s) Having Jurisdiction.
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of David
> Blackwell
> Sent: Thursday, December 29, 2011 12:31 PM
> To: [email protected]
> Subject: RE: Dwelling Unit- 13 vrs IBC defs
>
> Don't confuse yourself by using terms defined in one code or standard and
> applying that to another.
> The term is normally only good for that code or standard and are separate.
> Use the IBC definition when applying IBC rules and NFPA 13 definition when
> applying NFPA 13.
>
> I can go into detail/legal if you like but this brief explanation keeps it
> simple and to the point...
>
> [If I am wrong or missed something, someone will surely speak up (knowing
> the "forumites" who regularly post).]
>
>
> Respectfully,
>
>
> David W. S. Blackwell, II, PE, CFPE, CFI I Chief Engineer Office of State
> Fire Marshal SC Department of Labor, Licensing, & Regulation, 141
> Monticello Trail, Columbia, SC 29203
> Telephone: 803.896.9800 [Office] 803.896.9833 [Direct]
> Fax: 803.896.9806 [Office]
> Email:   [email protected]
> Website:  http://www.scfiremarshal.llronline.com/
>
>
> Please note that you can sign up to receive automatic information on SC
> Division of Fire and Life Safety current events, policies, laws and
> procedures by visiting our Web site at:
> http://www.scfiremarshal.llronline.com/
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of George
> Church
> Sent: Thursday, December 29, 2011 10:17 AM
> To: [email protected]
> Subject: Dwelling Unit- 13 vrs IBC defs
>
> NFPA 13-'07 defines a dwelling unit in 3.3.7 and specifically calls out
> "For
> purposes of this standard, dwelling unit includes hotel rooms,..." and
> there
> is no requirement for cooking facilities.
>
> 2009 IBC in 202, Definitions, Dwelling Unit. A single unit providing
> complete, independent living facilities for one or more persons, including
> permanent provisions for living, sleeping, eating, cooking and sanitation."
>
> So while the installation standard clearly states hotel rooms are intended
> to be protected as dwelling units, it seems that in order to qualify as
> dwelling units under the IBC, permanent cooking facilities must be present,
> and building codes trump installation standards.
>
> So does this mean when designing a system under #13 in a jurisdiction that
> adopted the IBC, we can't use dwelling unit rules from 13 in a hotel if the
> rooms don't contain a kitchen and bathroom?
> ]
> It may get cloudy when the IBC continues on to require QR or Residential
> sprinklers in Group R and I-1 dwelling units and sleeping units in 903.3.2
> (2).
>
>
> George L.  Church, Jr., CET
> Rowe Sprinkler Systems, Inc.
> PO Box 407, Middleburg, PA 17842
> 877-324-ROWE       570-837-6335 fax
> [email protected]
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Johnson,
> Duane (NIH/OD/ORS) [C]
> Sent: Thursday, December 29, 2011 10:00 AM
> To: [email protected]
> Subject: RE: NFPA 25 standpipe test
>
> It's a holiday week...all references below are from NFPA 25.
>
> -----Original Message-----
> From: Johnson, Duane (NIH/OD/ORS) [C]
> Sent: Thursday, December 29, 2011 9:54 AM
> To: [email protected]
> Subject: RE: NFPA 25 standpipe test
>
> ...that is 1998 edition of NFPA 25. sorry
>
> -----Original Message-----
> From: Johnson, Duane (NIH/OD/ORS) [C]
> Sent: Thursday, December 29, 2011 9:50 AM
> To: [email protected]
> Subject: RE: NFPA 25 standpipe test
>
> You must flow the system demand at time of design (14:6.3.1.3 2008 ed). The
> flow test must occur at the hyd most remote outlets (14:6.3.1.2).  You only
> need to do one flow test per zone (14:6.3.1.1). Your two sections do not
> necessarily mean two zones.
>
> Note also, if this is for Joint Commission, you will need to go back to the
> old codes.  To my knowledge, they are enforcing NFPA 101 2000
> edition...this
> means the 1998 edition of NFPA 14 is applicable.
>
> Duane Johnson, PE
> Program Manager
> Division of the Fire Marshal (Support Contractor) Office of Research
> Services National Institutes of Health
> 301-496-0487
>
> "Protecting Science - One Sprinkler at a Time"
>
> -----Original Message-----
> From: Todd Williams [mailto:[email protected]]
> Sent: Thursday, December 29, 2011 9:15 AM
> To: [email protected]
> Subject: NFPA 25 standpipe test
>
> I am working with a hospital with a total of 9 standpipes. There are
> standpipes that are both pre and post 1993. The original building is
> partially sprinklered and the new section is fully sprinklered.
>
> 1. Is the intent of NFPA 25 that multiple standpipes be flowed
> simultaneously to meet the 1250 gpm demand?
>
> 2. Should the two sections of the hospital be flow independent of each
> other?
>
> 3. If yes to 1 and 2, could the new section be flowed as a fully
> sprinklered
> building (thus 1000 gpm) as opposed to 1250?
>
> 4. How should i handle pipe schedule standpipes, if any exist?
>
> I haven't had to deal with 5 year standpipe tests before.
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860.535.2080
> www.fpdc.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111230/0e7c912e/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to