I agree with Ken, when we do in racks systems they have a separate control 
valve at the riser - best practice. However I believe he is asking the 
following (this is an example): If you have two overhead systems 40,000ft ۛ² 
each and you have two 40,000ft ۛ² in rack systems, one under each overhead 
system, can you feed rack system number one from the main from overhead system 
number two and vice versa? I believe you could do this since you wouldn't be 
cutting off the in racks and overhead system in the same area. If you cut off 
overhead system number one you would be cutting off the inracks under number 
two at the same time.

Is this practical or best way to do this, I say not but acceptable - I feel it 
would be. Someone may want a control valve and drain valve to the rack system 
after the split so if you needed to work on the rack system alone you could.

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax 
(731) 267-4853 cell
www.keyfireprotection.com
 

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Roland Huggins
Sent: Wednesday, February 01, 2012 12:22 PM
To: [email protected]
Subject: Re: What's wrong with this?

I've always been of the opinion that the standard is written around  
addressing a single system (except where explicitly allowed).  As  
such, I would say he could not use the adjacent system.  Ken Wagoner  
already pointed out the reason for the separate control valves  
(limiting the area out of service while servicing or replacing in-rack  
sprinklers).

Roland

On Feb 1, 2012, at 9:58 AM, Bobby Gillett wrote:

> Yes, after rereading the question, the answers did get away a bit. I  
> believe
> his suggestion would be acceptable as long as it was balanced at the  
> point
> of connection.
>
> Bobby Gillett

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.1913 / Virus Database: 2109/4779 - Release Date: 02/01/12

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to