Once again, and not disagreeing with Ken's comments regarding good
practice, the question wasn't about good practice but about rules.


On Wed, Feb 1, 2012 at 11:56 AM, Ron Greenman <[email protected]> wrote:

> I read adjacent to mean the overhead system over (adjacent to) the racks
> in question (might be one, might be 40K sqft), not necessarily the one to
> either side. language is so slippery. Vince, what did you mean by adjacent?
>
>
> On Wed, Feb 1, 2012 at 10:54 AM, Bobby Gillett <
> [email protected]> wrote:
>
>> I agree with Ken, when we do in racks systems they have a separate
>> control valve at the riser - best practice. However I believe he is asking
>> the following (this is an example): If you have two overhead systems
>> 40,000ft ۛ² each and you have two 40,000ft ۛ² in rack systems, one under
>> each overhead system, can you feed rack system number one from the main
>> from overhead system number two and vice versa? I believe you could do this
>> since you wouldn't be cutting off the in racks and overhead system in the
>> same area. If you cut off overhead system number one you would be cutting
>> off the inracks under number two at the same time.
>>
>> Is this practical or best way to do this, I say not but acceptable - I
>> feel it would be. Someone may want a control valve and drain valve to the
>> rack system after the split so if you needed to work on the rack system
>> alone you could.
>>
>> Bobby Gillett
>> Sr. Project Manager
>> Key Fire Protection, Inc.
>> (731) 424-0130 office  (731) 424-9285 fax
>> (731) 267-4853 cell
>> www.keyfireprotection.com
>>
>>
>> -----Original Message-----
>> From: [email protected] [mailto:
>> [email protected]] On Behalf Of Roland Huggins
>> Sent: Wednesday, February 01, 2012 12:22 PM
>> To: [email protected]
>> Subject: Re: What's wrong with this?
>>
>> I've always been of the opinion that the standard is written around
>> addressing a single system (except where explicitly allowed).  As
>> such, I would say he could not use the adjacent system.  Ken Wagoner
>> already pointed out the reason for the separate control valves
>> (limiting the area out of service while servicing or replacing in-rack
>> sprinklers).
>>
>> Roland
>>
>> On Feb 1, 2012, at 9:58 AM, Bobby Gillett wrote:
>>
>> > Yes, after rereading the question, the answers did get away a bit. I
>> > believe
>> > his suggestion would be acceptable as long as it was balanced at the
>> > point
>> > of connection.
>> >
>> > Bobby Gillett
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> -----
>> No virus found in this message.
>> Checked by AVG - www.avg.com
>> Version: 2012.0.1913 / Virus Database: 2109/4779 - Release Date: 02/01/12
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
>
> [email protected]
>
> http://www.bates.ctc.edu/fireprotection/
>
> 253.680.7346
> 253.576.9700 (cell)
>
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC
>
> They are happy men whose natures sort with their vocations. -Francis
> Bacon, essayist, philosopher, and statesman (1561-1626)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120201/c883efdb/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to