We bought ours from these guys: http://www.fpscmi.com/
The big challenge I think is that a straight generator isn't really capable of 
doing this job while being reasonably sized, the way their system works is that 
it fills the system with regular air (in part this is required because of the 
NFPA mandated minimum system filling times), then purges and refills over time 
with concentrated nitrogen which displaces the oxygen.  Our systems are under 
3% once the cycling finishes.  Even so the Ingersol compressors are monsters 
and the systems weren't cheap...
 
Mike Morey, SET, CFPS
Sprinkler Designer
BMW Constructors, Inc.
O: 317.651.0596 | C: 317.586.8111
www.bmwc.com

________________________________

From: [email protected] on behalf of Tom Duross
Sent: Tue 2/21/2012 6:53 AM
To: Sprinklerforum
Subject: N2 Generator



Has anyone designed and installed a nitrogen generator for a dry system?  I
have some questions regarding listing, sizing, flow rate and pressure.

I'm wondering if the requirements are similar to air compressors with those
above parameters in particular, although I don't see a definitive yes or no
in the standard (2007 here).  So I guess maybe I'm looking for
opinions/advice.  I'm hoping to be replacing that old system I posted about
a month ago suspect of being effected by MIC.  Planning to have some lab
work done beforehand to ascertain requirements.



Thomas Duross

The Fire Pump Testing Company

11 Varney Street

Jamaica Plain, MA 02130

T 617-971-0700

F 617-524-7171

C 617-592-4236

[email protected]



-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120221/e1e92f4a/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


-------------- next part --------------
A non-text attachment was scrubbed...
Name: winmail.dat
Type: application/ms-tnef
Size: 5013 bytes
Desc: not available
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120221/c2dd3ec2/attachment.bin>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to