Which manufacturer has a listed one?

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax 
(731) 267-4853 cell
www.keyfireprotection.com
 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Richard Carr
Sent: Wednesday, February 22, 2012 6:38 AM
To: [email protected]
Subject: RE: max pipe length 

Ken, I have not seen any response to your question so thought I would
offer my opinion, I have seen them used in the past when a second layer
of sheetrock was installed but I don't like using more than one per
head, unless you calc them, I only know of one manufacturer that has a
listed one, brass ones are better, it has to do bad things to the head K
factor.

Richard Carr, SET
Branch Manager
Cox Fire Protection, Inc
904-781-8227
[email protected]

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ken Shuss
Sent: Tuesday, February 21, 2012 3:32 PM
To: [email protected]
Subject: max pipe length 

I have a client that has a cpvc sprinkler system in an office building.
They are removing the existing clg and installing a new one 3" lower.
Can I use 1/2" nipple extenders?  If so what is the max length that can
be used? 1"?   3"?







-- 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.1913 / Virus Database: 2113/4823 - Release Date: 02/21/12

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to