No, there isn't a provision where a certain flow rate or sprinkler spacing 
provides the equivalent protection of a fixed, passive, fire resistant 
construction method.


Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Dewayne Martinez
Sent: Thursday, April 12, 2012 4:48 PM
To: SprinklerFORUM
Subject: glass block floor - 1hr rating

Have a building where the architect wants to install a glass block floor
in lieu of an atrium opening but the floor needs to have a 1 hr rating.
Is there anywhere in the IBC/IFC/NFPA code that allows sprinkler
protection to provide the 1hr rating?

Thanks,

 

Dewayne Martinez

Design Build Fire Protection

262-784-7900 (w)

262-784-8401 (f)

414-349-0468 (cell)

 

 