The AHJ CAN accept it, he has no culpability.  The burden of proving it 
provides such an equivalent is on the guy Stamping the drawings.  Just by 
bumping up the hazard category and selecting a particular sprinkler doesn't 
prove anything.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Brad Casterline
Sent: Thursday, April 12, 2012 5:32 PM
To: [email protected]
Subject: RE: glass block floor - 1hr rating

I should have just tried to answer the question, but the answer is yes and
no, per IBC 2012 703.4, no to using sprinklers as equivalent, but yes
because the section shall not limit the powers of the building official to
accept it, which is where Steve's WAG and Craig's chopping block come in I
guess. :)

Brad
member: AFSA

-----Original Message-----
From: Steve Leyton [mailto:[email protected]] 
Sent: Thursday, April 12, 2012 4:06 PM
To: [email protected]
Subject: RE: glass block floor - 1hr rating

Based on ... ???   WAG science?   An interesting concept, but I wouldn't
go looking for an ICC ESR number ...

SL 




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brad
Casterline
Sent: Thursday, April 12, 2012 2:04 PM
To: [email protected]
Subject: RE: glass block floor - 1hr rating

I am aware of a similar situation where the AHJ accepted the use of Old
Style Heads (spray 40% up/60% down) AND bump the occupancy
classification from Light Hazard to Ordinary Hazard Group I.

-----Original Message-----
From: Dewayne Martinez [mailto:[email protected]]
Sent: Thursday, April 12, 2012 3:48 PM
To: SprinklerFORUM
Subject: glass block floor - 1hr rating

Have a building where the architect wants to install a glass block floor
in lieu of an atrium opening but the floor needs to have a 1 hr rating.
Is there anywhere in the IBC/IFC/NFPA code that allows sprinkler
protection to provide the 1hr rating?

Thanks,

 

Dewayne Martinez

Design Build Fire Protection

262-784-7900 (w)

262-784-8401 (f)

414-349-0468 (cell)

 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ment
s/20120412/eecaefc5/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to