Vince,

 

I checked the friction data Ron suggested and it hit me that your original
post was asking for a K Value, not K Factor! The closest thing I found was a
2.5" globe valve with a K Value of 6.1 for use in the formula hf=k(v^2/2g).
Since friction loss is proportional to the square of the velocity we cannot
use an equivalent feet for all flows. At 500 GPM I get k --what? = 130, and
C from the previous post = .7. Instead of reducing the area, we'll reduce h,
and also include the velocity head loss:

 

500/7.48/60=1.11 ft^3/sec, / .034 ft^2=32.77 ft/sec.
hf=(32.77^2/64.4)*6.1=101.7 ft (*.433=~44 PSI).

(flowing 250 GPM the Pf is 11 PSI).

Velocity head, hv=(32.77^2/64.4)=16.68 ft.

100 PSI/.433=231 feet, -(101.7+16.68)=112.62 ft. v=(2*32.2*112.62)^.5=85.16
ft/sec, *.034 ft^2=2.9 ft^3/sec, *7.48*60= Q=1,300 GPM, P=100 PSI, K=130.

"Theoretical": v=(2*32.2*231)^2=122 ft/sec*.034 ft^2=4.15
ft^3/sec*7.48*60=1,862 GPM. "C" = 1,300/1,862=.7 (for a 2.5 to 3" globe
valve flowing 500 GPM anyway, if my thinking is correct).

 

If anyone knows of an empirical K Value for a 2.5" hose valve please post
it. A PSI/GPM curve would work, we'll just run the numbers backwards and
come up with a K Value --what?

 

-----Original Message-----
From: Brad Casterline [mailto:[email protected]] 
Sent: Saturday, April 14, 2012 2:36 PM
To: 'Vince Sabolik'
Cc: [email protected]
Subject: RE: k -- WHAT?

 

Vince,

 

I get K=149.

Instead of Q=K*P^2, I used Q=vA, (Q)cubic feet per second equals (v)feet per

second times (A)

square feet.

A=PI*radius^2,=PI*((2.5"/12/2)^2)=.034 ft^2. This is the "theoretical" area,

and we have to reduce 

it proportional to the friction loss through the valve. For lack of a

friction vs. velocity curve 

for now we'll assume the flow characteristics are similar to a 2.5" hydrant

butt where C=.8. So 

A=.034*.8=.0272 ft^2.

To find the velocity we use The Law of Falling Bodies, v=sqrt(2gh). g=32.2

ft/sec^2. To get h in 

feet we IMPLY a pressure and divide it by .433, so that if we have 100 PSI

at the valve, 

h=100/.433=231 ft. Now, v=(2*32.2*231)^.5=122 ft/sec. Q=vA,=122 ft/sec*.0272

ft^2=3.32 ft^3/sec. 

K --what? in units useful to our gallon, minute, pound, programs becomes:

Q=3.32 ft^3/sec,*7.48 

gal/ft^3,*60 sec/minute=1,490 GPM. P=100 PSI PSI. K=Q/(P^.5)=149.

 

We worked this out off Forum when you posted it, but based on the replies, I

wanted to suggest this

to the Forum at large, hoping it will help someone sometime, if it is not

messed up. Also I just saw 

that Ron G posted a link to some friction loss data which might cure the .8

assumption, I'll check it out.

*******************************************

 

Good morning --

 

Anyone have an approximate K value for a 2½" hose valve?

 

 

 

 

Vince Sabolik, West Tech Fire Protection, Inc.

 

11351 Pearl Road / Strongsville, Ohio 44136 440 238-4800 Fax 440 238-4876

 

-------------- next part --------------

An HTML attachment was scrubbed...

URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120414/16e70c63/attachment.html>

_______________________________________________

Sprinklerforum mailing list

[email protected]

http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120416/4cfbb8ac/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to