Funny, my 1987 Edition 5-2.3.1 states: 
"Gridded dry-pipe systems shall not be installed."


David Autry

Meininger Fire Protection Inc.
2521 W L St. Suite No.4
Lincoln, Ne 68522
Voice (402) 466-2616
Fax (402) 466-2617
[email protected]

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Daniel Wilder
Sent: Monday, June 11, 2012 10:04 AM
To: [email protected]
Subject: RE: dry grid prohibition

http://dbase.firesprinkler.org:591/online_archives/tech_interps/FMPro?-db=in
formal-interps.fp5&-format=record_detail.htm&-lay=form&-recid=12629921&-find
all=

You asked the following question "What year did NFPA ban the use of gridded
dry pipe systems?" In response to your question, we have reviewed the 1989
and the 1991 Edition of NFPA 13 as the applicable standards. Our informal
interpretation is that the 1991 Edition of NFPA 13 was the first edition to
ban the use of a gridded dry pipe system. The 1989 NFPA 13, Subsection
5-2.3.1 "Volume Limitations" discusses gridded systems. Exception to 5-2.3.1
talks about the ability to exceed the maximum system volume of 750 gallons
for non-gridded systems. I did not have a copy of the 1989 Handbook
available but the 1987 Handbook had a commentary on Subsection 5-2.3.1
"Volume Limitations". The commentary to "Volume Limitations" discusses the
problem of excessive delays in water delivery for gridded dry systems. The
next NFPA 13 Edition following 1989 is the 1991. Under Subsection 3-2.3.1
"Volume Limitations" is Subsection 3-2.3.2 that states, "Gridded dry pipe
systems shall not be installed." This is the first occurrence in NFPA 13 for
the ban on gridded dry pipe systems. The commentary in the 1991 Handbook
state that in more the 90 percent of the installations of gridded dry pipe
systems, the times for delivering water to the inspector's test connection
were excessive. The commentary further state that in some cases it took as
long as 10 minutes for the water to be delivered to the inspectors test. In
conclusion, NFPA 13 up to the 1991 Edition allowed gridded dry pipe systems.
The 1991 Edition banned the use of gridded dry pipe systems

Dan
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Monday, June 11, 2012 7:56 AM
To: [email protected]
Subject: dry grid prohibition

Would anyone know when dry grids were taken out of NFPA 13? My recollection
is mid 1980's, but don't have a copy to check.

We've encountered a dry-pipe system installed circa 1999, purported to be in
accordance with NFPA 13- 1994 according to the signature of a NICET Level
IV, complete with little NICET symbol that looks like a seal....oh well.
But each of the four wings is protected by a small gridded system.

Can someone say whether or not dry grids were permitted in the 1994 edition
of 13?


George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to