And you have to determine what edition was in use by the jurisdiction at
the time of the installation.

On Mon, Jun 11, 2012 at 8:16 AM, Todd Williams <[email protected]> wrote:

> 1989 section 5.2.3.1 includes it in the last sentence. The other editions
> (at least later ones) had it as a separate section.
>
>
>
> At 11:03 AM 6/11/2012, you wrote:
> >
> http://dbase.firesprinkler.org:591/online_archives/tech_interps/FMPro?-db=informal-interps.fp5&-format=record_detail.htm&-lay=form&-recid=12629921&-findall=
> >
> >You asked the following question "What year did NFPA ban the use of
> gridded dry pipe systems?" In response to your question, we have reviewed
> the 1989 and the 1991 Edition of NFPA 13 as the applicable standards. Our
> informal interpretation is that the 1991 Edition of NFPA 13 was the first
> edition to ban the use of a gridded dry pipe system. The 1989 NFPA 13,
> Subsection 5-2.3.1 "Volume Limitations" discusses gridded systems.
> Exception to 5-2.3.1 talks about the ability to exceed the maximum system
> volume of 750 gallons for non-gridded systems. I did not have a copy of the
> 1989 Handbook available but the 1987 Handbook had a commentary on
> Subsection 5-2.3.1 "Volume Limitations". The commentary to "Volume
> Limitations" discusses the problem of excessive delays in water delivery
> for gridded dry systems. The next NFPA 13 Edition following 1989 is the
> 1991. Under Subsection 3-2.3.1 "Volume Limitations" is Subsection 3-2.3.2
> that states, "Gridded dry pipe systems shall not be install
>  ed." This is the first occurrence in NFPA 13 for the ban on gridded dry
> pipe systems. The commentary in the 1991 Handbook state that in more the 90
> percent of the installations of gridded dry pipe systems, the times for
> delivering water to the inspector's test connection were excessive. The
> commentary further state that in some cases it took as long as 10 minutes
> for the water to be delivered to the inspectors test. In conclusion, NFPA
> 13 up to the 1991 Edition allowed gridded dry pipe systems. The 1991
> Edition banned the use of gridded dry pipe systems
> >
> >Dan
> >
> >
> >-----Original Message-----
> >From: [email protected] [mailto:
> [email protected]] On Behalf Of George Church
> >Sent: Monday, June 11, 2012 7:56 AM
> >To: [email protected]
> >Subject: dry grid prohibition
> >
> >Would anyone know when dry grids were taken out of NFPA 13? My
> recollection is mid 1980's, but don't have a copy to check.
> >
> >We've encountered a dry-pipe system installed circa 1999, purported to be
> in accordance with NFPA 13- 1994 according to the signature of a NICET
> Level IV, complete with little NICET symbol that looks like a seal....oh
> well.  But each of the four wings is protected by a small gridded system.
> >
> >Can someone say whether or not dry grids were permitted in the 1994
> edition of 13?
> >
> >
> >George L.  Church, Jr., CET
> >Rowe Sprinkler Systems, Inc.
> >PO Box 407, Middleburg, PA 17842
> >877-324-ROWE       570-837-6335 fax
> >[email protected]
> >
> >
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860.535.2080
> www.fpdc.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120611/b5019145/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to