There is some guidance in the handbook to allow some "shadowing" from
partial height walls, ceiling fans, lights, and other architectual
featuers...but there is no way to cover every circumstance that will
occur in the real world so you really have to use some judgement.

Ask the inspector to stand with his back at the door and see when he can
and cannot see the sprinkler to determine the actual obstruction....line
of sight method. Then look at the area that is obstructed to determine
what if anything might be located in this space that might be burning. A
3-foot door will take up at least half of the space so there's really
nothing to protect in the obstructed area except the door and walls.

At worse, he will ask you to add another sprinkler on the other side of
the light fixture...so two sprinklers in the 5 x 5-foot entry. If that
seems like an overkill, then it probably is.
I vote for one sprinkler on a 6-inch drop nipple to clear the light
fixture.  :)
rick matsuda
city of dallas

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George
Church
Sent: Tuesday, June 12, 2012 1:48 PM
To: [email protected]
Subject: residential obstructions

I'm interested in feedback on a situation which is occurring fairly
frequently. The specifics may vary slightly, but the concept is always
the same.
In this case, I have an entranceway to an apartment. The entranceway is
roughly 5' x 5'. The ceiling has a soffit 7' above fin. floor. The main
apartment ceiling is 8' above fin. floor. There is a surface mounted
light near the center of the entranceway soffit. The light is 4 3/4"
deep at the center & is a domed light. The light is 1'-2" wide at the
base. I located a recessed pendent residential head within 6" of the
edge of the soffit. My head is 1'-10" from the center of the light. 
The local inspector has stated that I am in violation of 13-R.
Technically, he is correct. My head is too close to the light given the
difference in depth of the light vs. the depth of my deflector. Now,
there isn't enough room in the soffit to locate my head & meet code. My
head would be out of the soffit. Rather counter-productive to say the
least. In addition, if you look at the domed profile of the light, there
really isn't much of an obstruction. This, especially considering the
very small space that the head is covering. 
I ask for two things:
1. Input - as in, is my view valid or am I really missing the big
picture?
2. If I am correct, is there any documentation I can show the inspector?
( I have already offered to provide the text from the 13-R handbook. To
me, if you read the intent & history of the obstructions rules, this
really isn't an issue. It's extremely similar to the 400 cubic foot
closet exception.
 
Thank you in advance for any assistance that can be provided.
Regards,  
Michael G. Haley
Rowe Sprinkler Systems, Inc.
7993 US Hwy 522
PO Box 407
Middleburg, PA 17842
570-837-7647
570-837-6335 fax
[email protected]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to