Rick,
Hopefully that 6" drop nipple is a joke.  I remember, though it is more
blurry today than in the past, being a young lad who had to jump up and grab
everything in sight just to see if I could do it.  To reinforce this memory
I have four boys between 8 and 16 years and every one of them wants to see
if the can touch, hit, smack, or otherwise reach nearly every target in
sight.  In an apartment complex environment, that drop nipple wouldn't last
the first kid. Two sprinklers in a 5 x 5 entry would be ridiculous overkill.
The purpose in to get the occupants out of the building and surely that one
sprinkler, though partially obstructed on one side would do the trick.  

My thoughts,

Bob Knight, CET III
208-318-3057
www.firebyknight.com




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Matsuda,
Richard
Sent: Tuesday, June 12, 2012 1:17 PM
To: [email protected]
Subject: RE: residential obstructions


 There is some guidance in the handbook to allow some "shadowing" from
partial height walls, ceiling fans, lights, and other architectual
featuers...but there is no way to cover every circumstance that will occur
in the real world so you really have to use some judgement.

Ask the inspector to stand with his back at the door and see when he can and
cannot see the sprinkler to determine the actual obstruction....line of
sight method. Then look at the area that is obstructed to determine what if
anything might be located in this space that might be burning. A 3-foot door
will take up at least half of the space so there's really nothing to protect
in the obstructed area except the door and walls.

At worse, he will ask you to add another sprinkler on the other side of the
light fixture...so two sprinklers in the 5 x 5-foot entry. If that seems
like an overkill, then it probably is.
I vote for one sprinkler on a 6-inch drop nipple to clear the light fixture.
:) rick matsuda city of dallas

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Tuesday, June 12, 2012 1:48 PM
To: [email protected]
Subject: residential obstructions

I'm interested in feedback on a situation which is occurring fairly
frequently. The specifics may vary slightly, but the concept is always the
same.
In this case, I have an entranceway to an apartment. The entranceway is
roughly 5' x 5'. The ceiling has a soffit 7' above fin. floor. The main
apartment ceiling is 8' above fin. floor. There is a surface mounted light
near the center of the entranceway soffit. The light is 4 3/4"
deep at the center & is a domed light. The light is 1'-2" wide at the base.
I located a recessed pendent residential head within 6" of the edge of the
soffit. My head is 1'-10" from the center of the light. 
The local inspector has stated that I am in violation of 13-R.
Technically, he is correct. My head is too close to the light given the
difference in depth of the light vs. the depth of my deflector. Now, there
isn't enough room in the soffit to locate my head & meet code. My head would
be out of the soffit. Rather counter-productive to say the least. In
addition, if you look at the domed profile of the light, there really isn't
much of an obstruction. This, especially considering the very small space
that the head is covering. 
I ask for two things:
1. Input - as in, is my view valid or am I really missing the big picture?
2. If I am correct, is there any documentation I can show the inspector?
( I have already offered to provide the text from the 13-R handbook. To me,
if you read the intent & history of the obstructions rules, this really
isn't an issue. It's extremely similar to the 400 cubic foot closet
exception.
 
Thank you in advance for any assistance that can be provided.
Regards,
Michael G. Haley
Rowe Sprinkler Systems, Inc.
7993 US Hwy 522
PO Box 407
Middleburg, PA 17842
570-837-7647
570-837-6335 fax
[email protected]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.2180 / Virus Database: 2433/5064 - Release Date: 06/12/12

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to