Again...... Get rid of the curtain... Platform.....LH.  

Interesting how sprinklers are being argued over a curtain. Apparently they
aren't willing to do away with the curtain so there shouldn't be any issue
with the sprinklers.

File the appeal.

JD

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John Drucker
Sent: Wednesday, July 25, 2012 6:55 PM
To: [email protected]
Subject: Re: Stage/platform

Get rid of the curtain... LH.  Done
John Drucker - Mobile Email

----- Original Message -----
From: [email protected]
<[email protected]>
To: [email protected] <[email protected]>
Sent: Wed Jul 25 18:39:08 2012
Subject: RE: Stage/platform

Agree with you up to the end.  It's a Multi-Purpose building with a platform
that has a low ceiling and a horizontally closing curtain.  Not a performing
arts center or other "legitimate" stage type of facility.
So the building is used for PTA meetings, student assemblies and cafeteria
seating; it's a smaller A-group with a raised platform that faces the main
seating area, and I see the whole thing as light hazard.


The plans reviewer brought this up at the very end of a backcheck.  The
entire design is approved, and this wasn't a correction on the first plan
check. She brought it up right before we were to get signed off and it's a
big deal because the riser is at the other end of the building.
So this will change our piping plan and RCP over the platform, main size,
seismic bracing calc's, detail sheet, etc., etc.  That's why it's a BFD ...

SML




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John Drucker
Sent: Wednesday, July 25, 2012 3:32 PM
To: [email protected]
Subject: RE: Stage/platform


For example.......... An A-1 Theatre, IIA Construction, 1 story, 10,000 sf
in area, exit discharge at grade, occupant load of 299.  Does the building
need sprinklers ? 

903.2.1.1 Group A-1.

An automatic sprinkler system shall be provided for Group A-1 occupancies
where ONE of the following conditions exists: 
1.      The fire area exceeds 12,000 square feet (1115 m2).
2.      The fire area has an occupant load of 300 or more.
3.      The fire area is located on a floor other than the level of exit
discharge.
4.      The fire area contains a multitheater complex.

Lets add a Stage........

401.1 Detailed use and occupancy requirements.

In ADDITION to the occupancy and construction requirements in this code, the
provisions of this chapter apply to the special uses and occupancies
described herein.

[F] 410.6 Automatic sprinkler system.
Stages shall be equipped with an automatic fire-extinguishing system in
accordance with Chapter 9. Sprinklers shall be installed under the roof and
gridiron and under all catwalks and galleries over the stage.
Sprinklers shall be installed in dressing rooms, performer lounges, shops
and storerooms accessory to such stages.

Exceptions:
1.      Sprinklers are not required under stage areas less than 4 feet
(1219
mm) in clear height that are utilized exclusively for storage of tables and
chairs, provided the concealed space is separated from the adjacent spaces
by not less than 5/8-inch (15.9 mm) Type X gypsum board.
2.      Sprinklers are not required for stages 1,000 square feet (93 m2)
or
less in area and 50 feet (15 240 mm) or less in height where curtains,
scenery or other combustible hangings are not retractable vertically.
Combustible hangings shall be limited to a single main curtain, borders,
legs and a single backdrop.
3.      Sprinklers are not required within portable orchestra enclosures
on
stages.

So 410.6 could require the suppression of a stage in an otherwise
unsprinklered building.  Of course I really oversimplified this, obviously
means of egress figures into the equation.

If your building requires sprinklers based in 903, 410.6 is a mute point
since sprinklers are required throughout and the density based on the hazard
from 13, OH-2.

John


John Drucker, CET
Fire Protection Subcode Official
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ

Not the official position of any agency, association, committee or
otherwise.  Obtain required applications, permits, inspections and approvals
from Authority(s) Having Jurisdiction. 



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Wednesday, July 25, 2012 6:16 PM
To: [email protected]
Subject: RE: Stage/platform

But 410.6 excepts sprinklers where stages are less than 1,000 s.f. in area
and 50' high AND where there is only a "main curtain".  This is the fulcrum
of the widget: they're saying that the curtain that closes in front of the
stage is an "overhead  hanging curtain".   This thing has a t-bar
ceiling at
9'-0 or 10'-0.

We're putting in sprinklers either way as it's a fully sprinklered building
but absent a volume of "flag and bag" space above the stage,
OH-2 is a BFD and in my opinion not required on this particular application.


Steve 




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John Drucker
Sent: Wednesday, July 25, 2012 3:10 PM
To: [email protected]
Subject: RE: Stage/platform

2006 IBC Commentary......................

Platform

"Platforms are raised areas that are used for public performances and
presentations that EXCEPT FOR LIGHTING DO NOT INCORPORATE ANY OVERHEAD
HANGING CURTAINS, DROPS, SCENERY OR STAGE EFFECTS."

 
OVERHEAD HANGING CURTAINS..... It's a stage.  

Sprinklers.... 410.6
Standpipes (You're favorite) .... 410.7

Hope that helps,

John Drucker, CET
Fire Protection Subcode Official
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ

Not the official position of any agency, association, committee or
otherwise.  Obtain required applications, permits, inspections and approvals
from Authority(s) Having Jurisdiction. 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Wednesday, July 25, 2012 1:59 PM
To: [email protected]
Subject: Stage/platform

Friends, Romans, Forumite and Drucker:

I have a plans reviewer with whom we are dancing about on the subject of
defining a "platform" vs. a "stage".  Probably the largest part of the
conversation has to do with "overhead hanging curtains".  The definition of
a stage is basically a space within a building used for entertainment or
presentations that includes "overhead hanging curtains, drops,
scenery or stage effects other than lighting and sound."   

My take is that this space in an elementary school MP buildings is a
platform because it only has lighting and sound overhead.  Their take is
that it's a stage because it has a curtain that can be drawn across its
front.   Anyone have a more specific definition or code citation for
what constitutes an overhead hanging curtain?

Steve Leyton



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity
to which it is addressed and may contain information that is privileged and
confidential, nor is it, unless specifically stated, intended to be relied
upon by any person or persons other than the individual or entity named
above and no warranties or representations are made or intended to persons
or entities not named above.  If the reader is not the intended recipient,
you are hereby notified that any dissemination, distribution or copying of
this communication is strictly prohibited.  If you have received this
communication in error, please notify us immediately by telephone, return
this message to the address above and delete all copies.  Thank you.

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120725/9e59c125/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to