> Again, I'm looking at an older version of 101, but it talks specifically to
> the Platform by stating, "A.3.149.  The raised area within a building used
> for the presentation of music, plays, or other entertainment" and
> "A.3.3.149.  Platforms also include the head tables for special guest; that
> raised area for lectures and speakers; .... and for similar purposes wherein
> there are no overhead drops, pieces of scenery, or stage affects other than
> lighting and a screening valance.  A platform is not intended to be
> prohibited from using a curtain as a valance to screen or hide the electric
> conduit, lighting track, or similar fixtures, nor is a platform prohibited
> from using curtains that are used to obscure the back wall of the stage;  a
> curtain between the auditorium and the stage (grand or house curtain), a
> maximum of four leg drops; or a valance to screen lights, plumbing, and
> similar equipment from view." 
> 
> The OH design criteria appears to kick in when a platform is no longer a
> platform and it becomes a legitimate stage.  There are specifics that
> trigger the protection requirements such as area (1000 sf), height (50'),
> and vertically retractable scenery.
> 
> A small platform that has curtains is not a stage and therefore does not
> need to be treated and protected as such.
> 
> 
> Bob Knight, CET III
> 208-318-3057
> www.firebyknight.com
> 
> 
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Steve Leyton
> Sent: Thursday, July 26, 2012 8:27 AM
> To: [email protected]
> Subject: RE: Stage/platform
> 
> You kmow, that's really well put.  Same idea with a meeting room that has
> moving partitions.
> 
> Steve
> 
> "[email protected]" <[email protected]> wrote:
> 
> Do floor to ceiling curtains in an office with 10 ft.  ceiling change the
> office to OH?
> 
> Ron Fletcher
> Aero Automatic
> Phoenix, AZ
> 
> 
> 
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of John Drucker
> Sent: Wednesday, July 25, 2012 3:55 PM
> To: [email protected]
> Subject: Re: Stage/platform
> 
> Get rid of the curtain... LH.  Done
> John Drucker - Mobile Email
> 
> ----- Original Message -----
> From: [email protected]
> <[email protected]>
> To: [email protected] <[email protected]>
> Sent: Wed Jul 25 18:39:08 2012
> Subject: RE: Stage/platform
> 
> Agree with you up to the end.  It's a Multi-Purpose building with a platform
> that has a low ceiling and a horizontally closing curtain.  Not a performing
> arts center or other "legitimate" stage type of facility.
> So the building is used for PTA meetings, student assemblies and cafeteria
> seating; it's a smaller A-group with a raised platform that faces the main
> seating area, and I see the whole thing as light hazard.
> 
> 
> The plans reviewer brought this up at the very end of a backcheck.  The
> entire design is approved, and this wasn't a correction on the first plan
> check. She brought it up right before we were to get signed off and it's a
> big deal because the riser is at the other end of the building.
> So this will change our piping plan and RCP over the platform, main size,
> seismic bracing calc's, detail sheet, etc., etc.  That's why it's a BFD ...
> 
> SML
> 
> 
> 
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of John Drucker
> Sent: Wednesday, July 25, 2012 3:32 PM
> To: [email protected]
> Subject: RE: Stage/platform
> 
> 
> For example.......... An A-1 Theatre, IIA Construction, 1 story, 10,000 sf
> in area, exit discharge at grade, occupant load of 299.  Does the building
> need sprinklers ?
> 
> 903.2.1.1 Group A-1.
> 
> An automatic sprinkler system shall be provided for Group A-1 occupancies
> where ONE of the following conditions exists:
> 1.    The fire area exceeds 12,000 square feet (1115 m2).
> 2.    The fire area has an occupant load of 300 or more.
> 3.    The fire area is located on a floor other than the level of exit
> discharge.
> 4.    The fire area contains a multitheater complex.
> 
> Lets add a Stage........
> 
> 401.1 Detailed use and occupancy requirements.
> 
> In ADDITION to the occupancy and construction requirements in this code, the
> provisions of this chapter apply to the special uses and occupancies
> described herein.
> 
> [F] 410.6 Automatic sprinkler system.
> Stages shall be equipped with an automatic fire-extinguishing system in
> accordance with Chapter 9. Sprinklers shall be installed under the roof and
> gridiron and under all catwalks and galleries over the stage.
> Sprinklers shall be installed in dressing rooms, performer lounges, shops
> and storerooms accessory to such stages.
> 
> Exceptions:
> 1.    Sprinklers are not required under stage areas less than 4 feet
> (1219
> mm) in clear height that are utilized exclusively for storage of tables and
> chairs, provided the concealed space is separated from the adjacent spaces
> by not less than 5/8-inch (15.9 mm) Type X gypsum board.
> 2.    Sprinklers are not required for stages 1,000 square feet (93 m2)
> or
> less in area and 50 feet (15 240 mm) or less in height where curtains,
> scenery or other combustible hangings are not retractable vertically.
> Combustible hangings shall be limited to a single main curtain, borders,
> legs and a single backdrop.
> 3.    Sprinklers are not required within portable orchestra enclosures
> on
> stages.
> 
> So 410.6 could require the suppression of a stage in an otherwise
> unsprinklered building.  Of course I really oversimplified this, obviously
> means of egress figures into the equation.
> 
> If your building requires sprinklers based in 903, 410.6 is a mute point
> since sprinklers are required throughout and the density based on the hazard
> from 13, OH-2.
> 
> John
> 
> 
> John Drucker, CET
> Fire Protection Subcode Official
> Fire/Building/Electrical Inspector
> Fire Marshals Office
> Borough of Red Bank, NJ
> 
> Not the official position of any agency, association, committee or
> otherwise.  Obtain required applications, permits, inspections and approvals
> from Authority(s) Having Jurisdiction.
> 
> 
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Steve Leyton
> Sent: Wednesday, July 25, 2012 6:16 PM
> To: [email protected]
> Subject: RE: Stage/platform
> 
> But 410.6 excepts sprinklers where stages are less than 1,000 s.f. in area
> and 50' high AND where there is only a "main curtain".  This is the fulcrum
> of the widget: they're saying that the curtain that closes in front of the
> stage is an "overhead  hanging curtain".   This thing has a t-bar
> ceiling at
> 9'-0 or 10'-0.
> 
> We're putting in sprinklers either way as it's a fully sprinklered building
> but absent a volume of "flag and bag" space above the stage,
> OH-2 is a BFD and in my opinion not required on this particular application.
> 
> 
> Steve
> 
> 
> 
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of John Drucker
> Sent: Wednesday, July 25, 2012 3:10 PM
> To: [email protected]
> Subject: RE: Stage/platform
> 
> 2006 IBC Commentary......................
> 
> Platform
> 
> "Platforms are raised areas that are used for public performances and
> presentations that EXCEPT FOR LIGHTING DO NOT INCORPORATE ANY OVERHEAD
> HANGING CURTAINS, DROPS, SCENERY OR STAGE EFFECTS."
> 
> 
> OVERHEAD HANGING CURTAINS..... It's a stage.
> 
> Sprinklers.... 410.6
> Standpipes (You're favorite) .... 410.7
> 
> Hope that helps,
> 
> John Drucker, CET
> Fire Protection Subcode Official
> Fire/Building/Electrical Inspector
> Fire Marshals Office
> Borough of Red Bank, NJ
> 
> Not the official position of any agency, association, committee or
> otherwise.  Obtain required applications, permits, inspections and approvals
> from Authority(s) Having Jurisdiction.
> 
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Steve Leyton
> Sent: Wednesday, July 25, 2012 1:59 PM
> To: [email protected]
> Subject: Stage/platform
> 
> Friends, Romans, Forumite and Drucker:
> 
> I have a plans reviewer with whom we are dancing about on the subject of
> defining a "platform" vs. a "stage".  Probably the largest part of the
> conversation has to do with "overhead hanging curtains".  The definition of
> a stage is basically a space within a building used for entertainment or
> presentations that includes "overhead hanging curtains, drops, scenery or
> stage effects other than lighting and sound."
> 
> My take is that this space in an elementary school MP buildings is a
> platform because it only has lighting and sound overhead.  Their take is
> that it's a stage because it has a curtain that can be drawn across its
> front.   Anyone have a more specific definition or code citation for
> what constitutes an overhead hanging curtain?
> 
> Steve Leyton
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> 
> CONFIDENTIAL AND PROPRIETARY:
> This email message is intended only for the use of the individual or entity
> to which it is addressed and may contain information that is privileged and
> confidential, nor is it, unless specifically stated, intended to be relied
> upon by any person or persons other than the individual or entity named
> above and no warranties or representations are made or intended to persons
> or entities not named above.  If the reader is not the intended recipient,
> you are hereby notified that any dissemination, distribution or copying of
> this communication is strictly prohibited.  If you have received this
> communication in error, please notify us immediately by telephone, return
> this message to the address above and delete all copies.  Thank you.
> 
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL:
> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachme
> nts/20120725/9e59c125/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> -----
> No virus found in this message.
> Checked by AVG - www.avg.com
> Version: 2012.0.2197 / Virus Database: 2437/5155 - Release Date: 07/25/12
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to