NFPA makes no such distinction.  It's a reactive standard that says, IF
you have to sprinkler a "stage" then this is the criteria.  IF you have
a proscenium, here is the criteria.   You are repeating the same
platitude - what in the IBC makes it a stage if the only curtain is the
one that draws closed between the platform and the seating area.

Back to Phelps' point:  If I have a conference room of 3,000 sq. ft.
with a soffit down the middle for a demountable partition wall system,
so I have to arbitrarily upgrade that room (or half of it) to OH because
I can draw a curtain or wall between the two 1,500 sq. ft. subdivided
spaces?


SML




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of njarendt
tds.net
Sent: Thursday, July 26, 2012 10:25 AM
To: [email protected]
Subject: Re: RE: Stage/platform

It is a difference between the codes.  The IBC makes it simple it is a
stage it is the NFPA that creates a distinction.  You need to know how
the specific state wants it addressed and that is ny the codes the
individual state adopts and then customizes.
On Jul 26, 2012 11:22 AM, "Steve Leyton" <[email protected]>
wrote:

> I'm really trying to pull something tangible out of this discussion so
> please bear with me.   You stated, " If you are in an IBC state it is
a
> stage."  Why?  A platform allows for performances, a platform allows 
> for lighting and sound.  A platform DOESN'T allow for overhead stuff
...
> what I'm reaching for is that line - do you think it's the curtain
that
> closes in front of the state?   If so, are you agreeing with the
interp
> that it's an "overhead hanging curtain"?   Do you not see a
distinction
> between curtains that are retractable and a curtain that is on a fixed

> track?
>
>
> Steve Leyton
>
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of David
E.
> Herbert
> Sent: Thursday, July 26, 2012 8:56 AM
> To: [email protected]
> Subject: Re: Stage/platform
>
> Remember that the IBC has different definitions. If you are in an IBC 
> state it is a stage. If you are in an NFPA 101 state, it may not be a 
> stage. And if you are lucky enough to be in a state that uses both IBC

> and 101,,,,,,,,, at least in the one I work in now, the most stringent

> applies, which in this case appears to be IBC so I guess we are back 
> to being a stage....
>
> It was so much easier working with only one code in my former life in 
> the State of Drucker.
>
> Dave Herbert
> now in the Sunshine State
>
> From: Bob <[email protected]>
> To: [email protected]
> Sent: Thursday, July 26, 2012 11:35 AM
> Subject: RE: Stage/platform
>
> Again, I'm looking at an older version of 101, but it talks 
> specifically to the Platform by stating, "A.3.149.  The raised area 
> within a building used for the presentation of music, plays, or other 
> entertainment" and "A.3.3.149.  Platforms also include the head tables

> for special guest; that raised area for lectures and speakers; .... 
> and for similar purposes wherein there are no overhead drops, pieces 
> of scenery, or stage affects other than lighting and a screening 
> valance.  A platform is not intended to be prohibited from using a 
> curtain as a valance to screen or hide the electric conduit, lighting 
> track, or similar fixtures, nor is a platform prohibited from using 
> curtains that are used to obscure the back wall of the stage;  a 
> curtain between the auditorium and the stage (grand or house curtain),

> a maximum of four leg drops; or a valance to screen lights, plumbing,
and similar equipment from view."
>
> The OH design criteria appears to kick in when a platform is no longer

> a platform and it becomes a legitimate stage.  There are specifics 
> that trigger the protection requirements such as area (1000 sf), 
> height (50'), and vertically retractable scenery.
>
> A small platform that has curtains is not a stage and therefore does 
> not need to be treated and protected as such.
>
>
> Bob Knight, CET III
> 208-318-3057
> www.firebyknight.com
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Steve 
> Leyton
> Sent: Thursday, July 26, 2012 8:27 AM
> To: [email protected]
> Subject: RE: Stage/platform
>
> You kmow, that's really well put.  Same idea with a meeting room that 
> has moving partitions.
>
> Steve
>
> "[email protected]" <[email protected]> wrote:
>
> Do floor to ceiling curtains in an office with 10 ft.  ceiling change 
> the office to OH?
>
> Ron Fletcher
> Aero Automatic
> Phoenix, AZ
>
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of John 
> Drucker
> Sent: Wednesday, July 25, 2012 3:55 PM
> To: [email protected]
> Subject: Re: Stage/platform
>
> Get rid of the curtain... LH.  Done
> John Drucker - Mobile Email
>
> ----- Original Message -----
> From: [email protected]
> <[email protected]>
> To: [email protected] 
> <[email protected]>
> Sent: Wed Jul 25 18:39:08 2012
> Subject: RE: Stage/platform
>
> Agree with you up to the end.  It's a Multi-Purpose building with a 
> platform that has a low ceiling and a horizontally closing curtain.  
> Not a performing arts center or other "legitimate" stage type of
facility.
> So the building is used for PTA meetings, student assemblies and 
> cafeteria seating; it's a smaller A-group with a raised platform that 
> faces the main seating area, and I see the whole thing as light
hazard.
>
>
> The plans reviewer brought this up at the very end of a backcheck.  
> The entire design is approved, and this wasn't a correction on the 
> first plan check. She brought it up right before we were to get signed

> off and it's a big deal because the riser is at the other end of the
building.
> So this will change our piping plan and RCP over the platform, main 
> size, seismic bracing calc's, detail sheet, etc., etc.  That's why 
> it's a BFD ...
>
> SML
>
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of John 
> Drucker
> Sent: Wednesday, July 25, 2012 3:32 PM
> To: [email protected]
> Subject: RE: Stage/platform
>
>
> For example.......... An A-1 Theatre, IIA Construction, 1 story, 
> 10,000 sf in area, exit discharge at grade, occupant load of 299.  
> Does the building need sprinklers ?
>
> 903.2.1.1 Group A-1.
>
> An automatic sprinkler system shall be provided for Group A-1 
> occupancies where ONE of the following conditions exists:
> 1.    The fire area exceeds 12,000 square feet (1115 m2).
> 2.    The fire area has an occupant load of 300 or more.
> 3.    The fire area is located on a floor other than the level of exit
> discharge.
> 4.    The fire area contains a multitheater complex.
>
> Lets add a Stage........
>
> 401.1 Detailed use and occupancy requirements.
>
> In ADDITION to the occupancy and construction requirements in this 
> code, the provisions of this chapter apply to the special uses and 
> occupancies described herein.
>
> [F] 410.6 Automatic sprinkler system.
> Stages shall be equipped with an automatic fire-extinguishing system 
> in accordance with Chapter 9. Sprinklers shall be installed under the 
> roof and gridiron and under all catwalks and galleries over the stage.
> Sprinklers shall be installed in dressing rooms, performer lounges, 
> shops and storerooms accessory to such stages.
>
> Exceptions:
> 1.    Sprinklers are not required under stage areas less than 4 feet
> (1219
> mm) in clear height that are utilized exclusively for storage of 
> tables and chairs, provided the concealed space is separated from the 
> adjacent spaces by not less than 5/8-inch (15.9 mm) Type X gypsum
board.
> 2.    Sprinklers are not required for stages 1,000 square feet (93 m2)
> or
> less in area and 50 feet (15 240 mm) or less in height where curtains,

> scenery or other combustible hangings are not retractable vertically.
> Combustible hangings shall be limited to a single main curtain, 
> borders, legs and a single backdrop.
> 3.    Sprinklers are not required within portable orchestra enclosures
> on
> stages.
>
> So 410.6 could require the suppression of a stage in an otherwise 
> unsprinklered building.  Of course I really oversimplified this, 
> obviously means of egress figures into the equation.
>
> If your building requires sprinklers based in 903, 410.6 is a mute 
> point since sprinklers are required throughout and the density based 
> on the hazard from 13, OH-2.
>
> John
>
>
> John Drucker, CET
> Fire Protection Subcode Official
> Fire/Building/Electrical Inspector
> Fire Marshals Office
> Borough of Red Bank, NJ
>
> Not the official position of any agency, association, committee or 
> otherwise.  Obtain required applications, permits, inspections and 
> approvals from Authority(s) Having Jurisdiction.
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Steve 
> Leyton
> Sent: Wednesday, July 25, 2012 6:16 PM
> To: [email protected]
> Subject: RE: Stage/platform
>
> But 410.6 excepts sprinklers where stages are less than 1,000 s.f. in 
> area and 50' high AND where there is only a "main curtain".  This is 
> the fulcrum of the widget: they're saying that the curtain that closes

> in front of the stage is an "overhead  hanging curtain".  This thing 
> has a t-bar ceiling at
> 9'-0 or 10'-0.
>
> We're putting in sprinklers either way as it's a fully sprinklered 
> building but absent a volume of "flag and bag" space above the stage,
> OH-2 is a BFD and in my opinion not required on this particular 
> application.
>
>
> Steve
>
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of John 
> Drucker
> Sent: Wednesday, July 25, 2012 3:10 PM
> To: [email protected]
> Subject: RE: Stage/platform
>
> 2006 IBC Commentary......................
>
> Platform
>
> "Platforms are raised areas that are used for public performances and 
> presentations that EXCEPT FOR LIGHTING DO NOT INCORPORATE ANY OVERHEAD

> HANGING CURTAINS, DROPS, SCENERY OR STAGE EFFECTS."
>
>
> OVERHEAD HANGING CURTAINS..... It's a stage.
>
> Sprinklers.... 410.6
> Standpipes (You're favorite) .... 410.7
>
> Hope that helps,
>
> John Drucker, CET
> Fire Protection Subcode Official
> Fire/Building/Electrical Inspector
> Fire Marshals Office
> Borough of Red Bank, NJ
>
> Not the official position of any agency, association, committee or 
> otherwise.  Obtain required applications, permits, inspections and 
> approvals from Authority(s) Having Jurisdiction.
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Steve 
> Leyton
> Sent: Wednesday, July 25, 2012 1:59 PM
> To: [email protected]
> Subject: Stage/platform
>
> Friends, Romans, Forumite and Drucker:
>
> I have a plans reviewer with whom we are dancing about on the subject 
> of defining a "platform" vs. a "stage".  Probably the largest part of 
> the conversation has to do with "overhead hanging curtains".  The 
> definition of a stage is basically a space within a building used for 
> entertainment or presentations that includes "overhead hanging 
> curtains, drops, scenery or stage effects other than lighting and
sound."
>
> My take is that this space in an elementary school MP buildings is a 
> platform because it only has lighting and sound overhead.  Their take 
> is that it's a stage because it has a curtain that can be drawn across

> its front.  Anyone have a more specific definition or code citation 
> for what constitutes an overhead hanging curtain?
>
> Steve Leyton
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
> CONFIDENTIAL AND PROPRIETARY:
> This email message is intended only for the use of the individual or 
> entity to which it is addressed and may contain information that is 
> privileged and confidential, nor is it, unless specifically stated, 
> intended to be relied upon by any person or persons other than the 
> individual or entity named above and no warranties or representations 
> are made or intended to persons or entities not named above.  If the 
> reader is not the intended recipient, you are hereby notified that any

> dissemination, distribution or copying of this communication is 
> strictly prohibited.  If you have received this communication in 
> error, please notify us immediately by telephone, return this message 
> to the address above and delete all copies.  Thank you.
>
> -------------- next part -------------- An HTML attachment was 
> scrubbed...
> URL:
> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/atta
> ch
> me
> nts/20120725/9e59c125/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> -----
> No virus found in this message.
> Checked by AVG - www.avg.com
> Version: 2012.0.2197 / Virus Database: 2437/5155 - Release Date:
> 07/25/12
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
>
>
>
>
>
> -------------- next part -------------- An HTML attachment was 
> scrubbed...
> URL:
> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/atta
> ch ments/20120726/071ffdcc/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20120726/e31c99b3/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to