I'm really trying to pull something tangible out of this discussion so
please bear with me.   You stated, " If you are in an IBC state it is a
stage."  Why?  A platform allows for performances, a platform allows for
lighting and sound.  A platform DOESN'T allow for overhead stuff ...
what I'm reaching for is that line - do you think it's the curtain that
closes in front of the state?   If so, are you agreeing with the interp
that it's an "overhead hanging curtain"?   Do you not see a distinction
between curtains that are retractable and a curtain that is on a fixed
track?   


Steve Leyton




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of David E.
Herbert
Sent: Thursday, July 26, 2012 8:56 AM
To: [email protected]
Subject: Re: Stage/platform

Remember that the IBC has different definitions. If you are in an IBC
state it is a stage. If you are in an NFPA 101 state, it may not be a
stage. And if you are lucky enough to be in a state that uses both IBC
and 101,,,,,,,,, at least in the one I work in now, the most stringent
applies, which in this case appears to be IBC so I guess we are back to
being a stage....
 
It was so much easier working with only one code in my former life in
the State of Drucker.
 
Dave Herbert
now in the Sunshine State
 
From: Bob <[email protected]>
To: [email protected]
Sent: Thursday, July 26, 2012 11:35 AM
Subject: RE: Stage/platform

Again, I'm looking at an older version of 101, but it talks specifically
to the Platform by stating, "A.3.149.  The raised area within a building
used for the presentation of music, plays, or other entertainment" and
"A.3.3.149.  Platforms also include the head tables for special guest;
that raised area for lectures and speakers; .... and for similar
purposes wherein there are no overhead drops, pieces of scenery, or
stage affects other than lighting and a screening valance.  A platform
is not intended to be prohibited from using a curtain as a valance to
screen or hide the electric conduit, lighting track, or similar
fixtures, nor is a platform prohibited from using curtains that are used
to obscure the back wall of the stage;  a curtain between the auditorium
and the stage (grand or house curtain), a maximum of four leg drops; or
a valance to screen lights, plumbing, and similar equipment from view." 

The OH design criteria appears to kick in when a platform is no longer a
platform and it becomes a legitimate stage.  There are specifics that
trigger the protection requirements such as area (1000 sf), height
(50'), and vertically retractable scenery.

A small platform that has curtains is not a stage and therefore does not
need to be treated and protected as such.


Bob Knight, CET III
208-318-3057
www.firebyknight.com



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve
Leyton
Sent: Thursday, July 26, 2012 8:27 AM
To: [email protected]
Subject: RE: Stage/platform

You kmow, that's really well put.  Same idea with a meeting room that
has moving partitions.

Steve

"[email protected]" <[email protected]> wrote:

Do floor to ceiling curtains in an office with 10 ft.  ceiling change
the office to OH?

Ron Fletcher
Aero Automatic
Phoenix, AZ




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John
Drucker
Sent: Wednesday, July 25, 2012 3:55 PM
To: [email protected]
Subject: Re: Stage/platform

Get rid of the curtain... LH.  Done
John Drucker - Mobile Email

----- Original Message -----
From: [email protected]
<[email protected]>
To: [email protected] <[email protected]>
Sent: Wed Jul 25 18:39:08 2012
Subject: RE: Stage/platform

Agree with you up to the end.  It's a Multi-Purpose building with a
platform that has a low ceiling and a horizontally closing curtain.  Not
a performing arts center or other "legitimate" stage type of facility.
So the building is used for PTA meetings, student assemblies and
cafeteria seating; it's a smaller A-group with a raised platform that
faces the main seating area, and I see the whole thing as light hazard.


The plans reviewer brought this up at the very end of a backcheck.  The
entire design is approved, and this wasn't a correction on the first
plan check. She brought it up right before we were to get signed off and
it's a big deal because the riser is at the other end of the building.
So this will change our piping plan and RCP over the platform, main
size, seismic bracing calc's, detail sheet, etc., etc.  That's why it's
a BFD ...

SML




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John
Drucker
Sent: Wednesday, July 25, 2012 3:32 PM
To: [email protected]
Subject: RE: Stage/platform


For example.......... An A-1 Theatre, IIA Construction, 1 story, 10,000
sf in area, exit discharge at grade, occupant load of 299.  Does the
building need sprinklers ?

903.2.1.1 Group A-1.

An automatic sprinkler system shall be provided for Group A-1
occupancies where ONE of the following conditions exists:
1.    The fire area exceeds 12,000 square feet (1115 m2).
2.    The fire area has an occupant load of 300 or more.
3.    The fire area is located on a floor other than the level of exit
discharge.
4.    The fire area contains a multitheater complex.

Lets add a Stage........

401.1 Detailed use and occupancy requirements.

In ADDITION to the occupancy and construction requirements in this code,
the provisions of this chapter apply to the special uses and occupancies
described herein.

[F] 410.6 Automatic sprinkler system.
Stages shall be equipped with an automatic fire-extinguishing system in
accordance with Chapter 9. Sprinklers shall be installed under the roof
and gridiron and under all catwalks and galleries over the stage.
Sprinklers shall be installed in dressing rooms, performer lounges,
shops and storerooms accessory to such stages.

Exceptions:
1.    Sprinklers are not required under stage areas less than 4 feet
(1219
mm) in clear height that are utilized exclusively for storage of tables
and chairs, provided the concealed space is separated from the adjacent
spaces by not less than 5/8-inch (15.9 mm) Type X gypsum board.
2.    Sprinklers are not required for stages 1,000 square feet (93 m2)
or
less in area and 50 feet (15 240 mm) or less in height where curtains,
scenery or other combustible hangings are not retractable vertically.
Combustible hangings shall be limited to a single main curtain, borders,
legs and a single backdrop.
3.    Sprinklers are not required within portable orchestra enclosures
on
stages.

So 410.6 could require the suppression of a stage in an otherwise
unsprinklered building.  Of course I really oversimplified this,
obviously means of egress figures into the equation.

If your building requires sprinklers based in 903, 410.6 is a mute point
since sprinklers are required throughout and the density based on the
hazard from 13, OH-2.

John


John Drucker, CET
Fire Protection Subcode Official
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ

Not the official position of any agency, association, committee or
otherwise.  Obtain required applications, permits, inspections and
approvals from Authority(s) Having Jurisdiction.



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve
Leyton
Sent: Wednesday, July 25, 2012 6:16 PM
To: [email protected]
Subject: RE: Stage/platform

But 410.6 excepts sprinklers where stages are less than 1,000 s.f. in
area and 50' high AND where there is only a "main curtain".  This is the
fulcrum of the widget: they're saying that the curtain that closes in
front of the stage is an "overhead  hanging curtain".  This thing has a
t-bar ceiling at
9'-0 or 10'-0.

We're putting in sprinklers either way as it's a fully sprinklered
building but absent a volume of "flag and bag" space above the stage,
OH-2 is a BFD and in my opinion not required on this particular
application.


Steve




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John
Drucker
Sent: Wednesday, July 25, 2012 3:10 PM
To: [email protected]
Subject: RE: Stage/platform

2006 IBC Commentary......................

Platform

"Platforms are raised areas that are used for public performances and
presentations that EXCEPT FOR LIGHTING DO NOT INCORPORATE ANY OVERHEAD
HANGING CURTAINS, DROPS, SCENERY OR STAGE EFFECTS."


OVERHEAD HANGING CURTAINS..... It's a stage.

Sprinklers.... 410.6
Standpipes (You're favorite) .... 410.7

Hope that helps,

John Drucker, CET
Fire Protection Subcode Official
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ

Not the official position of any agency, association, committee or
otherwise.  Obtain required applications, permits, inspections and
approvals from Authority(s) Having Jurisdiction.


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve
Leyton
Sent: Wednesday, July 25, 2012 1:59 PM
To: [email protected]
Subject: Stage/platform

Friends, Romans, Forumite and Drucker:

I have a plans reviewer with whom we are dancing about on the subject of
defining a "platform" vs. a "stage".  Probably the largest part of the
conversation has to do with "overhead hanging curtains".  The definition
of a stage is basically a space within a building used for entertainment
or presentations that includes "overhead hanging curtains, drops,
scenery or stage effects other than lighting and sound."

My take is that this space in an elementary school MP buildings is a
platform because it only has lighting and sound overhead.  Their take is
that it's a stage because it has a curtain that can be drawn across its
front.  Anyone have a more specific definition or code citation for what
constitutes an overhead hanging curtain?

Steve Leyton



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or
entity to which it is addressed and may contain information that is
privileged and confidential, nor is it, unless specifically stated,
intended to be relied upon by any person or persons other than the
individual or entity named above and no warranties or representations
are made or intended to persons or entities not named above.  If the
reader is not the intended recipient, you are hereby notified that any
dissemination, distribution or copying of this communication is strictly
prohibited.  If you have received this communication in error, please
notify us immediately by telephone, return this message to the address
above and delete all copies.  Thank you.

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
me
nts/20120725/9e59c125/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.2197 / Virus Database: 2437/5155 - Release Date:
07/25/12

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum






 
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20120726/071ffdcc/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to