If you were in Rod's or Frozen Mark's neighborhood, where you need 180% 
concentrations to keep from freezing, I'd would argue that's reckless (and 
stupid). But if you're doing what NFPA said with the exception of it not being 
listed, I'd say until there is a listed one on the market the case could be 
made for continuing to do your business as you have, so long as you don't 
install the chance of explosion. We didn't stop installing fire pumps when #20 
said you need a PLD or VSD not a main relief truncating the supply in order to 
control excess churn pressure. But once a listed VSD and/or PLD was on the 
market, you should have switched over to using the listed product. Let's face 
it, haven't we, forever, been using the FM-Approved version of devices on FM 
jobs UNLESS NONE WAS AVAILABLE, in which case we used a UL listed version as 
the best we could do, and just what we all used if it was something that might 
not have needed- or with some oddball devices, that no one bothered to obtain- 
a UL listing either.


George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
g...@rowesprinkler.com



-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Dewayne Martinez
Sent: Tuesday, August 28, 2012 3:28 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Antifreeze Update

Thanks George, this is the same way we have been looking at it.  I was just 
wondering how the other contractors were handling the situation.  We know that 
our competition has not stopped using A/F yet and to bid these same buildings 
with dry sprinkler systems would cost us a lot of business.

-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
Sent: Tuesday, August 28, 2012 2:18 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Antifreeze Update

Dewayne, I had a short off-Forum debate with a friend when the AFSA release 
came out- citing we MUST address known problems when we're aware of them. I 
would debate that all day if I had the time.
On a parallel of when TIA's apply- CMS uses the 1999 edition on a certain date 
for nursing homes nationwide- or at least the ones that want Medicare/Medicaid 
reimbursements. Discussions direct with CMS made it clear that they enforce 
that date of the 1999 #13 and NOTHING ELSE matters. A case was attempted to be 
made that more recent editions of #13 are simply a conglomeration of all the 
TIAs from prior editions...it went nowhere with CMS, and the pitch was made by 
a nationally respected FPE and former member of the Standards Council. 

With that in mind, if I had the right to an opinion, it would be that unless 
your AHJ has adopted the TIAs they are not LAW. Now any fool of a contractor I 
would HOPE would not induce any antifreeze above the concentrations NFPA's 
testing didn't show as safe, since that COULD, again IMHO if I had one, bring 
in NEGLIGENCE, RECKLESS STUPIDITY, or other things that might land a sprinkler 
contractor in jail or without a business or other assets due to a judge or jury 
wondering how someone could kill another with a sprinkler system.

I no longer have any limits on how stupid I believe some of us contractors can 
be. Wish I could report a better state of the industry, but I can't. So I 
wouldn't worry about the lack of UL listing, but don't induce anything that 
goes BOOM and if I were your attorney, I'd be ok. But I'm a sprinkler 
contractor, and while I play PE without a license way too often, I don't give 
legal advice without caveats to consult with the guy who would be at the table 
with you trying to keep your butt out of jail. You can't make enough on any job 
to risk losing your freedom or all your assets.

George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
g...@rowesprinkler.com



-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Dewayne Martinez
Sent: Tuesday, August 28, 2012 12:27 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Antifreeze Update

I am a bit confused on the matter of when to apply these TIA's.  In 
jurisdictions using older editions of NFPA, the TIA would not
apply(correct?) but since we, as contractors, know of the hazards there is a 
potential liability issue if we don't follow the TIA?  We are currently 
purchasing a factory pre-mixed glycerin solution at the recommended NFPA ratio. 
 It appears from the NFPA 13 TIA that unless the manufacturer gets a UL of FM 
listing that we can no longer use this product, correct? 
Thanks,
Dewayne

-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Roland Huggins
Sent: Thursday, August 23, 2012 4:30 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Antifreeze Update

Yep except for those already under bid, a discussion with the AHJ to follow the 
NFPA 25 criteria is worth a shot.

Also when servicing an existing system, unless less than 30% for PG or 38% for 
Glycerin, you have to proof it's acceptable in order to keep it.
Well the ITM guy doesn't but he has to flag it for the owner with documentation 
showing he advised them of the issue and the owner has to obtain proof 
(deterministic risk assessment).

Roland


On Aug 23, 2012, at 2:14 PM, <rfletc...@aerofire.com> wrote:

> Is the bottom line no new NFPA 13 antifreeze systems for now?
>
> Ron Fletcher
> Aero - Phoneix

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to