Correct me if Im missing something but We do not meet the 10% and the separation and it is my understanding that the definition defines whats a miscellaneous storage and not just the 12.
3.9.1.14* Miscellaneous Storage. Storage that does not exceed 12 ft. (3.66 m) in height and is incidental to another occupancy use group. Such storage shall not constitute more than 10 percent of the building area or 4000 ft2 (372 m2) of the sprinklered area, whichever is greater. Such storage shall not exceed 1000 ft2 (93 m2) in one pile or area, and each such pile or area shall be separated from other storage areas by at least 25 ft (7.62 m). -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bob Sent: Wednesday, August 29, 2012 12:39 PM To: [email protected] Subject: RE: Multiple row rack question [2007] Joel, The area of storage is not the deciding factor in this case. 16.2.1.2, "Chapter 13 shall be acceptable for storage of Class I through IV commodities up to and including 12 ft in height". You use Table 13.2.1 to determine the protection criteria for your storage regardless of area. Bob Knight, CET III 208-318-3057 <http://www.firebyknight.com> www.firebyknight.com -----Original Message----- From: Joel Chaim <mailto:[mailto:[email protected]]> [mailto:[email protected]] Sent: Wednesday, August 29, 2012 10:17 AM To: <mailto:[email protected]> [email protected]; <mailto:[email protected]> [email protected] Subject: RE: Multiple row rack question [2007] I saw that but my issue is that the definition [3.9.1.14 of miscellaneous storage is limited to 10% and this job is a building of 100,000² -----Original Message----- From: <mailto:[email protected]> [email protected] <mailto:[mailto:[email protected]]> [mailto:[email protected]] On Behalf Of Bob Sent: Wednesday, August 29, 2012 12:12 PM To: <mailto:[email protected]> [email protected] Subject: RE: Multiple row rack question [2007] Joel, Look at 16.2.1.2. This directs you back to Chapter 13. Bob Knight, CET III 208-318-3057 <http://www.firebyknight.com> www.firebyknight.com -----Original Message----- From: <mailto:[email protected]> [email protected] <mailto:[mailto:[email protected]]> [mailto:[email protected]] On Behalf Of Joel Chaim Sent: Wednesday, August 29, 2012 9:23 AM To: <mailto:[email protected]> [email protected] Subject: Multiple row rack question [2007] I have a building that has multiple row racks and is less than 12' and we can't use miscellaneous storage because it exceeds the area, chapter 16 only has scenarios for over 12' can anybody guide me where to look? -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment s/20120829/3dc0a159/attachment.html> _______________________________________________ Sprinklerforum mailing list <mailto:[email protected]> [email protected] <http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum ----- No virus found in this message. Checked by AVG - <http://www.avg.com> www.avg.com Version: 2012.0.2197 / Virus Database: 2437/5233 - Release Date: 08/29/12 _______________________________________________ Sprinklerforum mailing list <mailto:[email protected]> [email protected] <http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum ----- No virus found in this message. Checked by AVG - <http://www.avg.com> www.avg.com Version: 2012.0.2197 / Virus Database: 2437/5233 - Release Date: 08/29/12 _______________________________________________ Sprinklerforum mailing list <mailto:[email protected]> [email protected] <http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120829/8e8eb0f0/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum