Joel,
You are not protecting miscellaneous storage, so the definition has no
bearing.  Simply, the design parameters from chapter 13 are being used for
Chapter 16 storage less than or equal to 12'.  The same is true for Chapter
14.

Thanks,

Bob Knight, CET III
208-318-3057
www.firebyknight.com




-----Original Message-----
From: Joel Chaim [mailto:[email protected]] 
Sent: Wednesday, August 29, 2012 10:45 AM
To: [email protected]; [email protected]
Subject: RE: Multiple row rack question [2007]

And what about the definition of miscellaneous storage [3.9.1.14]?

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bob
Sent: Wednesday, August 29, 2012 12:39 PM
To: [email protected]
Subject: RE: Multiple row rack question [2007]

Joel,
The area of storage is not the deciding factor in this case.  16.2.1.2,
"Chapter 13 shall be acceptable for storage of Class I through IV
commodities up to and including 12 ft in height".  You use Table 13.2.1 to
determine the protection criteria for your storage regardless of area.

Bob Knight, CET III
208-318-3057
www.firebyknight.com



-----Original Message-----
From: Joel Chaim [mailto:[email protected]]
Sent: Wednesday, August 29, 2012 10:17 AM
To: [email protected]; [email protected]
Subject: RE: Multiple row rack question [2007]

I saw that but my issue is that the definition [3.9.1.14] of miscellaneous
storage is limited to 10% and this job is a building of 100,000²

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bob
Sent: Wednesday, August 29, 2012 12:12 PM
To: [email protected]
Subject: RE: Multiple row rack question [2007]

Joel,
Look at 16.2.1.2.  This directs you back to Chapter 13.

Bob Knight, CET III
208-318-3057
www.firebyknight.com



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Joel Chaim
Sent: Wednesday, August 29, 2012 9:23 AM
To: [email protected]
Subject: Multiple row rack question [2007]

I have a building that has multiple row racks and is less than 12' and  we
can't use miscellaneous storage because it exceeds the area, chapter 16 only
has scenarios for over 12' can anybody guide me where to look?

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120829/3dc0a159/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.2197 / Virus Database: 2437/5233 - Release Date: 08/29/12

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.2197 / Virus Database: 2437/5233 - Release Date: 08/29/12

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.2197 / Virus Database: 2437/5233 - Release Date: 08/29/12

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to