Well I don't know how you get 30 minutes if only rocked on one side per:
11.2.3.3.3 To utilize the room design method, all rooms shall be enclosed with 
walls having a fire-resistance rating equal to the water supply duration 
indicated in Table 11.2.3.1.2.

And in #2 - 2,260 still isn't enough unless you meet the same rating issue 
wherever an additional 275 sq.ft. might be. 

I have used room design in these cases a couple times particularly where the 
water supply was an issue.  Imagine no three phase power and no water.  Cutting 
a small attic in half saves the day with a single phase pump and small tank. 

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation & Facilities Group
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN





-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Gregory Lindholm
Sent: Friday, August 31, 2012 1:41 PM
To: SprinklerFORUM
Subject: RE: Attic Remote Area


Yes, I was thinking about using the room design method. In this instance, there 
would be not reasonable was to remove the sheet rock in example #1, and pretty 
tough to do anything in example #2.
 
Is there any reason not to use the room design method here?

Greg Lindholm
 

> From: [email protected]
> To: [email protected]
> Subject: Re: Attic Remote Area
> Date: Fri, 31 Aug 2012 11:26:16 -0700
> 
> concur, we ignore even rated walls unless using room design method.
> 
> There is new guidance on how to address small subsystems (such as dry- 
> pipe on loading docks or preaction in computer room) in the 2013 
> edition of NFPA 13. This use to be a particularly tricky issue when 
> applying logic for an answer when the sub-system like a loading dock 
> uses spray sprinklers and the adjacent warehouse system uses ESFR.
> See the June issue of Sprinkler Age for more information.
> 
> Roland
> 
> 
> 
> On Aug 31, 2012, at 10:57 AM, Cahill, Christopher wrote:
> 
> > 1. Assuming they are the same system. Yes, where does it say you can 
> > reduce the area below 2,535? Getting the total area is almost a 
> > Cardinal rule. Only way out is room design method if it applies.
> > But that entails being reasonably sure the required walls will 
> > remain after the legendary cable guy comes through. One reason the 
> > room design method is flawed, owners can take down walls without 
> > even thinking sprinklers (as long as they are 6' apart). I guarantee 
> > during inspection no one knows if it room design or not.
> > I know we can't plan for the future.
> > 2. Same answer.
> >
> > Chris Cahill, PE*
> 
> -------------- next part -------------- An HTML attachment was 
> scrubbed...
> URL: 
> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/atta
> chments/20120831/1ff2322f/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
                                          
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120831/aaf31bdb/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to