Jarron,
        It is not a good practice to have a water service that far into a
building.  You may also want to check with the water purveyor and the
insurance company because they may not allow this due to the liability.  One
solution I have used is to rise up with the service at the outside wall and
run the supply in an accessible trench just below the floor to the
equipment.  We had an outside PIV to control the this section of pipe.  This
allows for the inspection and repair of the pipe if necessary.  This could
allow you to get the supply to the FDC back to the outside wall along with
the main drain.  We also were able to provide a flow switch, at the outside
wall,  to monitor this section of pipe. 
        Just a thought
        Dick
        

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jarron Gass
Sent: Thursday, September 13, 2012 8:38 AM
To: [email protected]
Subject: Shutoff at Service Entrance



Folks,

 

I am struggling with whether it is allowable by NFPA13, 2007 edition to have
approximately 100' of "underground" piping inside the building before the
shutoff.  In this situation, there is a meter pit outside of the building,
then the UG enters the building and goes up and across to the front of the
facility and connects into the fire sprinkler header.  There is no valve
immediately where the piping enters the building, or any means to monitor
flow.  My understanding is that this was a new UG to replace an old
dilapidated one.  I have not pinpointed anything in the code that tells me
this is not ok, however it just doesn't seem to be a good practice.  I
appreciate any guidance from anyone who might have dealt with a  similar
situation.

 

~Jarron  

 

Jarron J. Gass - J. & J. Fire Protection Co., Inc.

101 Powell Rd., Butler, PA 16002, (724) 586-6111, fax (724) 586-5151

emergency (724) 898-2481,  <mailto:[email protected]>
[email protected],  <http://www.jandjfire.com> www.jandjfire.com 

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120913/be989d05/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.gif
Type: image/gif
Size: 862 bytes
Desc: not available
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120913/be989d05/attachment.gif>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to