Had a situation similar to this once at an old NORAD Aircraft Hanger. 
6" UG piping was ran in a concrete crawl space between the hangers, all pump
rooms were located below grade. Piping rotted through at a coupling due to
an overhead mechanical leak and the joint came apart, by the time someone
realized what had happened one of the pump rooms had become completely
submerged.
Needless to say we were later contracted to install flow switches on these
lines. Seems like cheap insurance where there is a possibility of property
damage.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Thursday, September 13, 2012 8:57 PM
To: [email protected]
Subject: Re: Shutoff at Service Entrance

Jarron,

You're monitoring waterflow of sprinklers. As long as the waterflow detector
is before all the sprinklers, after the sprinkler control valve and before
the first split in the system. You seem to have anywhere along 100' of pipe
to locate the device. Unless there is a major savings in conduit and wire
that makes locating it away from the riser makes sense I'd keep it at the
riser since that's where we usually find them. There's nothing along the
100' of pipe to monitor.

On Thu, Sep 13, 2012 at 4:57 PM, Jarron Gass <[email protected]> wrote:

> My concern is probably shifting more to whether or not this should 
> have a flow switch for that portion of the piping.  I can accept that 
> there is a shutoff outside in the meter pit, but i feel like this should
be monitored.
>  That is probably more a want than a need.
>
> ~Jarron
>
> Sent from my Verizon Wireless Droid
>
> -----Original message-----
> From: [email protected]
> To: sprinklerforum@firesprinkler.**org 
> <[email protected]>
> Sent: Thu, Sep 13, 2012 22:12:31 GMT+00:00
> Subject: Re: Shutoff at Service Entrance
>
> Well for a real life situation where this exists, albeit in a very 
> large building in Kansas City --- picture a 1000 feet by 2000 feet
building.
> 10-inch fire mains running east-west and north-south through the 
> building with takeoffs for manifolded sprinkler systems of from 2-3 
> risers each, typically.  The mains are looped and fed by fire pumps.  Lots
of potential
> for a super flood if you postulate the main breaking.   Leaks, unless
> large, are not going to be picked up by a flow switch anyway.
>
> We also have the situation described where an underground lead-in 
> enters the building, goes up and overhead out to a manifold about a 
> 100 feet into the building - no valve at the outside wall, yard post 
> valve, but there is a drain at the low point at the exterior wall.
>
> It has been like this since 1942 and no major problems.  Yes pipe can 
> leak but 8 and 10-inch pipe won't rust through before the 6, 4, and
smaller pipe
> will.   Whether the code prohibits this or not, not sure how else you
would
> sprinkler a place like this.
>
> John Hoffman P.E. | Fire Protection Engineer | Facility Engineering 
> Services, KCP, LLC - Burns & McDonnell Engineering | National Nuclear 
> Security Administration's Kansas City Plant | Operated by Honeywell 
> FM&T |
> 2000 E. 95th St | Kansas City, MO  64131 | ph 816-997-7213 | 
> [email protected]
>
> ______________________________**_________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.**org <[email protected]>
> http://fireball.firesprinkler.**org/mailman/listinfo/**sprinklerforum<
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum>
>
> -------------- next part -------------- An HTML attachment was 
> scrubbed...
> URL: <http://fireball.**firesprinkler.org/mailman/**
> private/sprinklerforum/**attachments/20120913/e85ce981/**attachment.ht
> ml<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/at
> tachments/20120913/e85ce981/attachment.html>
> >
> ______________________________**_________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.**org <[email protected]>
> http://fireball.firesprinkler.**org/mailman/listinfo/**sprinklerforum<
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum>
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120913/db50818a/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to