I should clarify that the piping is steel schedule 10, my issue is that there is a significant distance between where it enters the building and where the initial shut off valve is located. There is a valve in a pit outside, so it is possible to shut it down, but there is no flow switch on this run of pipe to notify of water discharge.
Thanks, Jarron Jarron J. Gass - J. & J. Fire Protection Co., Inc. 101 Powell Rd., Butler, PA 16002, (724) 586-6111, fax (724) 586-5151 emergency (724) 898-2481, [email protected], www.jandjfire.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of ParsleyConsulting Sent: Thursday, September 13, 2012 10:29 AM To: [email protected] Subject: Re: Shutoff at Service Entrance To extend Roland's remarks, there is also language in the new edition of -13 (and -24) which limits the length that underground pipe can be run under the foundation without arching, trenching or isolation valves to no more than 10'-0" from the edge of the foundation. PARSLEY CONSULTING Ken Wagoner, SET 760.745.6181 voice 760.745.0537 fax [email protected] <mailto:[email protected]>e-mail www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>website On 9/13/2012 7:20 AM, Roland Huggins wrote: > You will not find anything saying the use fo underground pipe above > ground is NOT ok. That's not how it works. Underground pipe by > definition and allowed use per Table 10.1.1 can only be used > underground (as dictated by the title of the applicable sections and > listing when required). Allowed pipe material for above ground is > defined by section 6.3. > > There is a new allowance in the 2013 edition that will make an > exception for the stub-up to the system riser to be underground pipe. > > Roland > > On Sep 13, 2012, at 6:58 AM, Dick Culver wrote: > >> >> I am struggling with whether it is allowable by NFPA13, 2007 edition >> to have approximately 100' of "underground" piping inside the >> building before the shutoff. In this situation, there is a meter pit >> outside of the building, then the UG enters the building and goes up >> and across to the front of the facility and connects into the fire >> sprinkler header. There is no valve immediately where the piping >> enters the building, or any means to monitor flow. My understanding >> is that this was a new UG to replace an old dilapidated one. I have >> not pinpointed anything in the code that tells me this is not ok, >> however it just doesn't seem to be a good practice. I appreciate any >> guidance from anyone who might have dealt with a similar situation. >> >> >> >> ~Jarron >> >> > > -------------- next part -------------- An HTML attachment was > scrubbed... > URL: > <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/atta > chments/20120913/71ab1b7a/attachment.html> > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum