You can, not supposed to, but you can.
 I have never been able to get the same reading at each without using the
valves on the header. Each hose is going to lose differently regardless of
length. So you must always adjust the valves to get "equal" readings. (Equal
being relative to the bouncing of the gauge in use)

R/
Matt 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Cahill,
Christopher
Sent: Tuesday, October 02, 2012 11:12 AM
To: [email protected]
Subject: RE: Fire pump annual test (VALVES)

You can't open an OS&Y part way?  I did say the same set up.  So if you have
4 playpipes at the same elevation connected each with 50' of hose you are
good.  I suppose of you put a 90 deg kink in one of the hoses you no longer
have the same setup.  Throw in one shorter or longer hose and you no longer
have the same set up.  And anyway you still need to check the pitot of each
and maybe make some fine adjustments. 

Chris 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Matthew J.
Willis
Sent: Tuesday, October 02, 2012 9:59 AM
To: [email protected]
Subject: RE: Fire pump annual test (VALVES)

".  If you have the same setup on each valve and playpipe you can open all
the 2.5" valves first with no flow and throttle with the manifold valve as
all the playpipes should be the same. "



Unless your manifold valve is non-throttling (OS&Y). Even then, isn't each
hose lay different?

R/
Matt

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to