I would never put full pump pressure on a header that's normally empty or use hose gates to modulate either. Always modulate with the OS&Y or BV, keep the pump pressure in the system, who cares if you have 2) 18's, a 19 and a 17? Playpipes are only listed with the tips on (1-1/8") which is why we have more outlets than we need to test a pump, they're rated for 250 each (45 on a tip). Test lots of pumps and then buy hosemonsters, pitotless nozzles and a remote reader. You'll never go back to a pitot tube.
You can, not supposed to, but you can. I have never been able to get the same reading at each without using the valves on the header. Each hose is going to lose differently regardless of length. So you must always adjust the valves to get "equal" readings. (Equal being relative to the bouncing of the gauge in use) R/ Matt _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum