I have the 99 edition, but know it is the others...,

A 11.2.6.3 outlines the test procedure.

Plus, I believe you will find that most Gate Valves are not listed for
throttle duty, but must be either fully open or full closed. 

R/
Matt

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Tom Duross
Sent: Tuesday, October 02, 2012 7:15 PM
To: [email protected]
Subject: RE: Fire pump annual test (VALVES)

I would never put full pump pressure on a header that's normally empty or
use hose gates to modulate either.  Always modulate with the OS&Y or BV,
keep the pump pressure in the system, who cares if you have 2) 18's, a 19
and a 17?  Playpipes are only listed with the tips on (1-1/8") which is why
we have more outlets than we need to test a pump, they're rated for 250 each
(45 on a tip).  Test lots of pumps and then buy hosemonsters, pitotless
nozzles and a remote reader.  You'll never go back to a pitot tube.


You can, not supposed to, but you can.
 I have never been able to get the same reading at each without using the
valves on the header. Each hose is going to lose differently regardless of
length. So you must always adjust the valves to get "equal" readings. (Equal
being relative to the bouncing of the gauge in use)

R/
Matt 