N2 Blast #250.   2 1/2" replacement main x 100' with 500' of 1" branches.
Relatively small.  I2 5BRx2B bungalow. 120'x45'.
I talked about sizing these with their Engineer and got the impression they
size them for some 'expected' leakage plus the trickle you set the purge
valve to relieve.  I was told it could take up to 72 hours to achieve 79%
preferred concentration.  I really was impressed with the thought behind the
whole design of how it would basically ideally remove one aspect of that
corrosion triangle.  This system that we posted here about had some serious
turburcles and just blew through 1"-3" sch40 in about 6 places.  I was there
this afternoon taking a sample of N2, 79%.  I cheaped out and got the
handheld probe but they have a remote reader that can be put at the valve or
someone's office, cabled to the purge valve.
Range is huge and 600+ systems could be pricey but with a basic 30 minute
compressor and then switched over to a nitrogen purge, I can't imagine any
issues even if the ramp up to concentration took 2 weeks or more.  
The generator makes up to 70 PSI so it does need to be tamed, but even if we
left the compressor open to the system just in case the generator output
didn't keep up,  it would mean a burst of raw air behind the nitrogen into
the system.  I piped it from the generator to the tank, from the tank to the
AMD and to the DPV1 with a tee before the AMD taking the compressor output.
Everything is valved.  Right now today, compressor is valved off and solely
on N2.  I tripped it last week for the FD and it's been almost 7 days.  I'd
like to keep the compressor on but have to talk to them.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Friday, October 05, 2012 5:21 PM
To: [email protected]
Subject: RE: Air Supply

Mind sharing the system volume for that much generator $?
You well know the volume range is huge, and with electronic accelerators now
allowing reliably faster trip times, we've done some warehouse conversions
that were monstrous. The one I'm thinking of had FM blessing, and a high
pressure supply that got the delivery time needed, but I'm sure there are
lots of other systems, and we've seen em especially in recycled old mill
type buildings, where the Owner didn't want to pay for heat so there's a
bunch of 8" risers with 6" DPVs. Not that an 8" would make any difference in
delivery time in some low or medium pressure situations.
Tick   tick   tick   

George L.  Church, Jr., CET
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Tom Duross
Sent: Friday, October 05, 2012 4:20 PM
To: [email protected]
Subject: RE: Air Supply

George, the generator I bought with an autopurge valve for the line to the
ITV, a sensor for checking N2 concentration, storage tank, was $6800.  I'm
gambling on limited data here that this 10K investment on a system will save
my customer from having to replace 50K in pipe and fittings only 30 years
old (30 years or less from now, not to mention the inconvenience, details,
etc.).  Bottles are cheap but I was leery about a couple of 5000 PSI bombs
20' from bedrooms.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Friday, October 05, 2012 11:22 AM
To: Charles Thurston; [email protected]
Subject: RE: Air Supply

$
You've got a belt and suspenders cost for a customer who, by code, only
needs one. 
And it didn't have to be the more expensive N2 version.
So when presenting the idea of minimizing future corrosion, he's got the
following, grabbing $ out of the air:
1. plant air- $600 for an AMD
2. Compressor- $1500
3. Bottle and HP AMD- $3000
4. Generator- 15000
5. Gen and bottle- $18,000

I'm seriously just trying to illustrate order of magnitude, anyone else
doing bottles and generators now can chime in if I'm off by a factor of 5 or
10. But costs vary with system size etc.


George L.  Church, Jr., CET
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Charles
Thurston
Sent: Friday, October 05, 2012 11:07 AM
To: [email protected]
Subject: Re: Air Supply

Hello,

Use bottled nitrogen for the 30 minute refill time and the nitrogen
generator for the pressure maintenance of the system.

Friday, October 5, 2012, 10:55:28 AM, you wrote:

> Ron,

> I requested a technical interpretation from NFPA for that exact question.

> My question was:

> NFPA 13, 2010, 7.2.6.2.2 states; The air supply shall have a capacity 
> capable of restoring normal air pressure in the system within 30 minutes.

> It does not state that the system shall be restored to normal system 
> pressure in 30 minutes. It states that the air supply shall be capable 
> of restoring the system to normal pressure in 30 minutes.

> My question is, If you can prove through calculations that the air 
> supply is capable of restoring normal pressure in 30 minutes, would it 
> be acceptable to actually take longer than 30 minutes to restore 
> normal
pressure?

> The purpose for the delayed fill time would be to use a nitrogen 
> generator as a pressure source instead of an air compressor. If an 
> empty system was initially pressurized with nitrogen, that would 
> eliminate the purging process that would be necessary if the system 
> was first pressurized with air and then the air slowly replaced by 
> nitrogen over time. This would help to slow any oxygen corrosion that 
> might be initiated if the system was filled with air.

>  Membrane type oxygen generators work by forcing air into a membrane 
> that separates the nitrogen from the oxygen. The CFM output of a 
> nitrogen generator is about 50% less than the CFM of the air 
> compressor supplying the nitrogen generator. The nitrogen generator 
> has a bypass loop so the system could be filled directly from the 
> compressor if desired. This is similar to the fill and maintain modes 
> of an Air Maintenance Device.


> Their response was:

> The intent of NFPA 13, 2010 edition §7.2.6.2.2 is to provide a 
> guideline which will protect the owner of the system from someone 
> installing an undersized compressor which would render systems out of 
> service for elongated periods of time while increasing service costs.
> The compressor is not required to be listed, in fact - a compressor is 
> not required.  The compressed gas supply may be from a reliable plant 
> air source or nitrogen tanks with a regulator.  The committee intent 
> is to have the system returned to service within the 30 minute 
> timeframe - regardless of the source for compressed air or nitrogen.
> It is assumed that a nitrogen generator (or other approved compressed
> gas) will provide nitrogen over the subsequent hours of operation and 
> replace the air used for initial charging.

>  


> Regards,
>  
> mike
>  
> Mike Henke CET
> Sprinkler Product Manager
> 314-595-6740 direct
> [email protected]
> www.pottersignal.com
>  
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Ron 
> Greenman
> Sent: Friday, October 05, 2012 9:19 AM
> To: [email protected]
> Subject: Re: Air Supply

> I'm curious where the 30 minute fill came from. Convenience to FDs? 
> I'd certainly not want my highly paid and trained engine company 
> hanging around for a couple of extra hours to watch the system fill.
> But if I'm likely have the service guy from the sprinkler company, or 
> even my owned trained maintenance, hanging around, and I'm willing to 
> pay for him to watch the paint dry, and I'm so concerned with my 
> system as to have bought a nitrogen generator instead of using that 
> nasty moisture holding air, why not ignore

> that code section? Or is the 30 minute rule there just because we 
> needed a

> definitive time frame and 30 minutes sounded reasonable at the time? 
> Or is

> there another, more compelling reason? Curious minds want to know.

> On Fri, Oct 5, 2012 at 6:07 AM, Tom Duross <[email protected]> wrote:

>> Most generators, if not all, have a nitrogen storage tank.  The one I 
>> used put out 70 PSI requiring an AMD and we still had a riser mount 
>> air compressor because the generator could not fill in 30 minutes.
>> They're interconnected and valved.
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Roland 
>> Huggins
>> Sent: Thursday, October 04, 2012 5:44 PM
>> To: [email protected]
>> Subject: Re: Air Supply
>>
>> If you use nitrogen (7.6.2.7)  it now kicks you over to 7.2.6.5 
>> (Automatic Air Maintenance).  Must admit, I see no reason to use an 
>> air tank and plenty not to (as George already said).  I'd say an air 
>> cylinder would be not different than a nitrogen cylinder when it 
>> comes to requiring an AMD.  If you do not have a low pressure alarm, 
>> the pressure gauge has to be checked weekly instead of monthly.  Now 
>> that dry pipe system have to have an air

>> leakage test performed every 3 years, there shouldn't be any systems 
>> (or at least as many) needing a compressor running full time to keep 
>> it from tripping.
>>
>> Roland
>>
>> On Oct 4, 2012, at 12:54 PM, Cahill, Christopher wrote:
>>
>> > Looking over a job where the EOR wants to use cylinders to supply 
>> > the air for a dry system.  There is plenty of power to the building 
>> > so that's not the issue.  They are showing lab air cylinders from 
>> > both air (NC) and nitrogen (NO) into an AMD into the system.  I get 
>> > automatic air is not required.  But I'm seeing NFPA 13
>> > '12-7.2.6.5.1 limiting air supply when AUTOMATIC to dependable shop 
>> > system or a compressor.  I don't see bottles being allowed.  Or 
>> > that is to say I don't see bottles as being a dependable shop system.
>> >
>> > I assume some of you have done bottles for the air to a dry system?
>> > As I read you can have them if someone manually opens a valve and 
>> > refills the system when needed?  Of course this is even confusing.
>> > Is there something on a manual fill system that requires daily 
>> > checking?  Or are they relying on the low pressure alarm to note 
>> > when time to refill?  Actually, the low pressure alarm isn't even 
>> > required,

>> > right, so are they waiting for a system trip to know when to add air?
>> >
>> > If manual is allowed isn't an AMD off a bottle a little better but 
>> > not

>> > quite the full blown compressor?  Why would they restrict the 
>> > middle on the order of worst to best?
>> >
>> > Who wants to straighten me out 'cuz none of us here have ever seen 
>> > bottles used on a system?
>> >
>> > Chris Cahill, PE*
>> > Senior Fire Protection Engineer, Aviation & Facilities Group Burns 
>> > & McDonnell
>> >
>> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>






--
Best regards,
 Charles                            mailto:[email protected]

 Confidentiality Notice: This e-mail message, including any attachments, is
for the sole purpose of the intended recipients and may contain confidential
and privileged information.  Any unauthorized review, use, disclosure or
distribution is prohibited.  If you are not the intended recipient, please
contact  the sender by reply e-mail and destroy all copies of the original
message.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to