Travis-
I was reading up on the BlazeMaster series and it's listed for exposed 
construction with certain heads, I always thought you could only use it if it 
was concealed?

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Travis Mack
Sent: Wednesday, December 19, 2012 3:42 PM
To: [email protected]
Subject: Re: NFPA13 & CPVC

We use plastic in quite a few places. I have done many offices that were done 
as a retrofit (non combustible construction) in CPVC.  It can be challenging 
for TI work over the years.

If the attic is wet and you can use Tyco BB/SD/HIP/AP sprinklers, then you can 
use CPVC in the attic as well.


Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

On 12/19/2012 1:20 PM, Brian Harris wrote:
> Travis-
> Will do, but in a nut shell there's nothing in NFPA that precludes it is 
> there? This got me thinking, what are the down sides to using it more often 
> if it's not exposed construction, ie: Offices etc.
>
> Brian Harris, CET
> BVS Systems Inc.
> bvssytemsinc.com
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Travis
> Mack
> Sent: Wednesday, December 19, 2012 3:17 PM
> To: [email protected]
> Subject: Re: NFPA13 & CPVC
>
> Check the CPVC data sheet for how you have the building construction and 
> sprinkler protection and how it relates to CPVC listings.
>
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> 480-505-9271
> fax: 866-430-6107
> email:[email protected]
>
> On 12/19/2012 1:13 PM, Brian Harris wrote:
>> I'm working on an adult day care that is being designed to NFPA-13, per 
>> 6.3.6.1 (2007) I'm free to use CPVC on the main floor and then use steel for 
>> the attic correct?
>>
>> Brian Harris, CET
>> BVS Systems Inc.
>> Sprinkler Division
>> bvssystemsinc.com<http://bvssystemsinc.com/>
>> Phone: 704.896.9989
>> Fax: 704.896.1935
>>
>> -------------- next part -------------- An HTML attachment was
>> scrubbed...
>> URL:
>> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/att
>> a chments/20121219/cf334e92/attachment.html>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to