Curtis, Thanks for the info... Brian Harris, CET BVS Systems Inc. bvssytemsinc.com
-----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Wednesday, December 19, 2012 4:28 PM To: [email protected] Subject: RE: NFPA13 & CPVC NFPA 13 (6.3.6.2) and 13R (5.2.2.3) limit CPVC to use in primarily light hazard areas, non-exposed, based on its listing (usually for light hazard). You CAN protect an ordinary hazard area with the same CPVC, providing the area does not exceed 400 s.f. When using CPVC in interstitial spaces, the Tyco CC1 type heads are indicated. There are very stringent rules for head positioning in that scenario, so you'll need to refer to the cut sheets. We've never utilized CPVC in a wet attic system; however, if you are running CPVC for the protection of the floor below, then the Tyco attic line of sprinklers are acceptable to protect the piping as long as the proper insulating techniques are employed. It is also stated that the insulation in this case is to protect the plastic piping; not for freeze protection. This has been our experience. Keep in mind that NFPA 13 typically defers to the manufacturers cut sheets on how and where certain fire sprinkler components can be used, and the component may be used according with how it was tested and approved through U.L. (sometimes beyond the general requirements of the standard.) Curtis Tower Central Fire Protection -----Original Message----- From: Brian Harris [mailto:[email protected]] Sent: Wednesday, December 19, 2012 3:02 PM To: [email protected] Subject: RE: NFPA13 & CPVC Travis- Sounds good, thanks for the input. Brian Harris, CET BVS Systems Inc. bvssytemsinc.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Travis Mack Sent: Wednesday, December 19, 2012 4:00 PM To: [email protected] Subject: Re: NFPA13 & CPVC The listings have been greatly expanded over the years. Be sure to check the current listings for applications. Many don't realize the extent of places CPVC can and can not be used. Travis Mack, SET MFP Design, LLC 2508 E Lodgepole Drive Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:[email protected] On 12/19/2012 1:47 PM, Brian Harris wrote: > Travis- > I was reading up on the BlazeMaster series and it's listed for exposed construction with certain heads, I always thought you could only use it if it was concealed? > > Brian Harris, CET > BVS Systems Inc. > bvssytemsinc.com > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Travis > Mack > Sent: Wednesday, December 19, 2012 3:42 PM > To: [email protected] > Subject: Re: NFPA13 & CPVC > > We use plastic in quite a few places. I have done many offices that > were done as a retrofit (non combustible construction) in CPVC. It can be challenging for TI work over the years. > > If the attic is wet and you can use Tyco BB/SD/HIP/AP sprinklers, then > you can use CPVC in the attic as well. > > > Travis Mack, SET > MFP Design, LLC > 2508 E Lodgepole Drive > Gilbert, AZ 85298 > 480-505-9271 > fax: 866-430-6107 > email:[email protected] > > On 12/19/2012 1:20 PM, Brian Harris wrote: >> Travis- >> Will do, but in a nut shell there's nothing in NFPA that precludes it >> is there? This got me thinking, what are the down sides to using it more often if it's not exposed construction, ie: Offices etc. >> >> Brian Harris, CET >> BVS Systems Inc. >> bvssytemsinc.com >> >> -----Original Message----- >> From: [email protected] >> [mailto:[email protected]] On Behalf Of Travis >> Mack >> Sent: Wednesday, December 19, 2012 3:17 PM >> To: [email protected] >> Subject: Re: NFPA13 & CPVC >> >> Check the CPVC data sheet for how you have the building construction >> and sprinkler protection and how it relates to CPVC listings. >> >> Travis Mack, SET >> MFP Design, LLC >> 2508 E Lodgepole Drive >> Gilbert, AZ 85298 >> 480-505-9271 >> fax: 866-430-6107 >> email:[email protected] >> >> On 12/19/2012 1:13 PM, Brian Harris wrote: >>> I'm working on an adult day care that is being designed to NFPA-13, >>> per 6.3.6.1 (2007) I'm free to use CPVC on the main floor and then use steel for the attic correct? >>> >>> Brian Harris, CET >>> BVS Systems Inc. >>> Sprinkler Division >>> bvssystemsinc.com<http://bvssystemsinc.com/> >>> Phone: 704.896.9989 >>> Fax: 704.896.1935 >>> >>> -------------- next part -------------- An HTML attachment was >>> scrubbed... >>> URL: >>> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/at >>> t a chments/20121219/cf334e92/attachment.html> >>> _______________________________________________ >>> Sprinklerforum mailing list >>> [email protected] >>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum