NFPA 13 (6.3.6.2) and 13R (5.2.2.3) limit CPVC to use in primarily light hazard 
areas, non-exposed, based on its listing (usually for light hazard).
You CAN protect an ordinary hazard area with the same CPVC, providing the area 
does not exceed 400 s.f.

When using CPVC in interstitial spaces, the Tyco CC1 type heads are indicated.  
There are very stringent rules for head positioning in that scenario, so you'll 
need to refer to the cut sheets.

We've never utilized CPVC in a wet attic system; however, if you are running 
CPVC for the protection of the floor below, then the Tyco attic line of 
sprinklers are acceptable to protect the piping as long as the proper 
insulating techniques are employed.  It is also stated that the insulation in 
this case is to protect the plastic piping; not for freeze protection.
This has been our experience.

Keep in mind that NFPA 13 typically defers to the manufacturers cut sheets on 
how and where certain fire sprinkler components can be used, and the component 
may be used according with how it was tested and approved through U.L. 
(sometimes beyond the general requirements of the standard.)

Curtis Tower
Central Fire Protection



-----Original Message-----
From: Brian Harris [mailto:[email protected]]
Sent: Wednesday, December 19, 2012 3:02 PM
To: [email protected]
Subject: RE: NFPA13 & CPVC

Travis-
Sounds good, thanks for the input.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Travis Mack
Sent: Wednesday, December 19, 2012 4:00 PM
To: [email protected]
Subject: Re: NFPA13 & CPVC

The listings have been greatly expanded over the years.  Be sure to check the 
current listings for applications.  Many don't realize the extent of places 
CPVC can and can not be used.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

On 12/19/2012 1:47 PM, Brian Harris wrote:
> Travis-
> I was reading up on the BlazeMaster series and it's listed for exposed
construction with certain heads, I always thought you could only use it if it 
was concealed?
>
> Brian Harris, CET
> BVS Systems Inc.
> bvssytemsinc.com
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Travis
> Mack
> Sent: Wednesday, December 19, 2012 3:42 PM
> To: [email protected]
> Subject: Re: NFPA13 & CPVC
>
> We use plastic in quite a few places. I have done many offices that
> were
done as a retrofit (non combustible construction) in CPVC.  It can be 
challenging for TI work over the years.
>
> If the attic is wet and you can use Tyco BB/SD/HIP/AP sprinklers, then
> you
can use CPVC in the attic as well.
>
>
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> 480-505-9271
> fax: 866-430-6107
> email:[email protected]
>
> On 12/19/2012 1:20 PM, Brian Harris wrote:
>> Travis-
>> Will do, but in a nut shell there's nothing in NFPA that precludes it
>> is
there? This got me thinking, what are the down sides to using it more often if 
it's not exposed construction, ie: Offices etc.
>>
>> Brian Harris, CET
>> BVS Systems Inc.
>> bvssytemsinc.com
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Travis
>> Mack
>> Sent: Wednesday, December 19, 2012 3:17 PM
>> To: [email protected]
>> Subject: Re: NFPA13 & CPVC
>>
>> Check the CPVC data sheet for how you have the building construction
>> and
sprinkler protection and how it relates to CPVC listings.
>>
>> Travis Mack, SET
>> MFP Design, LLC
>> 2508 E Lodgepole Drive
>> Gilbert, AZ 85298
>> 480-505-9271
>> fax: 866-430-6107
>> email:[email protected]
>>
>> On 12/19/2012 1:13 PM, Brian Harris wrote:
>>> I'm working on an adult day care that is being designed to NFPA-13,
>>> per
6.3.6.1 (2007) I'm free to use CPVC on the main floor and then use steel for 
the attic correct?
>>>
>>> Brian Harris, CET
>>> BVS Systems Inc.
>>> Sprinkler Division
>>> bvssystemsinc.com<http://bvssystemsinc.com/>
>>> Phone: 704.896.9989
>>> Fax: 704.896.1935
>>>
>>> -------------- next part -------------- An HTML attachment was
>>> scrubbed...
>>> URL:
>>> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/at
>>> t a chments/20121219/cf334e92/attachment.html>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to