Travis-
Sounds good, thanks for the input.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Travis Mack
Sent: Wednesday, December 19, 2012 4:00 PM
To: [email protected]
Subject: Re: NFPA13 & CPVC

The listings have been greatly expanded over the years.  Be sure to check the 
current listings for applications.  Many don't realize the extent of places 
CPVC can and can not be used.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

On 12/19/2012 1:47 PM, Brian Harris wrote:
> Travis-
> I was reading up on the BlazeMaster series and it's listed for exposed 
> construction with certain heads, I always thought you could only use it if it 
> was concealed?
>
> Brian Harris, CET
> BVS Systems Inc.
> bvssytemsinc.com
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Travis
> Mack
> Sent: Wednesday, December 19, 2012 3:42 PM
> To: [email protected]
> Subject: Re: NFPA13 & CPVC
>
> We use plastic in quite a few places. I have done many offices that were done 
> as a retrofit (non combustible construction) in CPVC.  It can be challenging 
> for TI work over the years.
>
> If the attic is wet and you can use Tyco BB/SD/HIP/AP sprinklers, then you 
> can use CPVC in the attic as well.
>
>
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> 480-505-9271
> fax: 866-430-6107
> email:[email protected]
>
> On 12/19/2012 1:20 PM, Brian Harris wrote:
>> Travis-
>> Will do, but in a nut shell there's nothing in NFPA that precludes it is 
>> there? This got me thinking, what are the down sides to using it more often 
>> if it's not exposed construction, ie: Offices etc.
>>
>> Brian Harris, CET
>> BVS Systems Inc.
>> bvssytemsinc.com
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Travis
>> Mack
>> Sent: Wednesday, December 19, 2012 3:17 PM
>> To: [email protected]
>> Subject: Re: NFPA13 & CPVC
>>
>> Check the CPVC data sheet for how you have the building construction and 
>> sprinkler protection and how it relates to CPVC listings.
>>
>> Travis Mack, SET
>> MFP Design, LLC
>> 2508 E Lodgepole Drive
>> Gilbert, AZ 85298
>> 480-505-9271
>> fax: 866-430-6107
>> email:[email protected]
>>
>> On 12/19/2012 1:13 PM, Brian Harris wrote:
>>> I'm working on an adult day care that is being designed to NFPA-13, per 
>>> 6.3.6.1 (2007) I'm free to use CPVC on the main floor and then use steel 
>>> for the attic correct?
>>>
>>> Brian Harris, CET
>>> BVS Systems Inc.
>>> Sprinkler Division
>>> bvssystemsinc.com<http://bvssystemsinc.com/>
>>> Phone: 704.896.9989
>>> Fax: 704.896.1935
>>>
>>> -------------- next part -------------- An HTML attachment was
>>> scrubbed...
>>> URL:
>>> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/at
>>> t a chments/20121219/cf334e92/attachment.html>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to