2 is all required in your example, well if you want to return to service. 

The heat cooling cycle of the glass bulbs are repeated cycles to very near 
operating temperature as I understand it.  One more cycle if it takes 100's or 
more cycles won't make a difference.  The first 99 are the problem. 

On the creep of solder its sustained temperatures near operation as I 
understand it.  This is a problem not a single fire. 

On the acid - well smoke comes in all flavors.  I'm certainly no chemist but 
with that logic why are we not replacing the structural components or the 
plumbing etc.?  Weren't they also damaged by the acid smoke?  I think where 
acid is an issue is in sensitive electronics.  Think of the difference in 
surface area.   And I don't understand the burn/smoke radius part.  The burn 
radius of a sprinkler controlled fire is on the order of 1 to ten's of feet.  
The smoke is often the entire building.  Not sure you need to go next door and 
replace sprinkler head to get 2 rings past, lol.  

What I typically see is out of an abundance of caution replace the fused heads 
and the first ring around.  But I don't think it has any technical merit. Once 
the fitter is there a couple more heads is cheap to make everyone feel good.  
In the end I wouldn't balk if you replace the 2 and if someone pays you for 
more, good for you.  

Good discussion item.  Often we don't get truly new things to banter about on 
this forum. 

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation & Facilities Group
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ben Young
Sent: Thursday, January 17, 2013 11:41 AM
To: [email protected]
Subject: Replacing heads after a fire

This was a hypothetical question asked by one of our inspectors the other day, 
and I did not know the answer.  Thought I would see if anyone else here might 
know where this is written in black and white.

Say you have a large room with 20+ heads, or an open warehouse area.  The 
building is fully sprinkled, and everything else is normal / SOP.

They have a fire in this room/area, and lets say, two heads activate and 
control the fire.

The question is, how many of the heads do you have to replace?  Is there a code 
requirements for this that exists?  I found some anecdotal evidence from 
someone in the industry with more experience than I, but the only thing close I 
could find in the codes was the NFPA 25 stuff relating to loading on sprinkler 
heads.

I looked at NFPA's list of codes online, and saw some that may have some 
information on this (NFPA 902 and 904) but they were withdrawn in 2001, and I 
cannot view them online.

Obviously from a liability standpoint, you would want to replace as many of the 
heads as possible, if not all of them, but what if you had a 500K SQFT 
warehouse that was all open, would you want to replace all of them?

Here's the information that I got from my friend who's been around a while.
-If they're link heads, you want to probably replace all the heads, since the 
acids in the smoke will impact the solder -Look at the burn/smoke radius from 
the fire, and replace the heads around this area for the next two rings of 
sprinkler heads.

He couldn't tell me where this came from, it was just the way it was always 
done.

Is there a hard and fast rule for this?  Is it an insurance carrier or head 
manufacturer judgement call?  Would rapid heating and cooling cause glass bulbs 
to weaken or micro-fracture down the road?


Thanks,


Benjamin Young
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130117/93248633/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to