a couple things:

1)...past editions. (me, right after I hit send)

2) 2012 IBC Code and Commentary, Vol. 1, pg. 9-39 (Mr. Cahill, off Forum) 

-----Original Message-----
From: Brad Casterline [mailto:[email protected]] 
Sent: Wednesday, January 23, 2013 2:49 PM
To: [email protected]
Subject: RE: manual vs automatic standpipes

Matt,

Check page 9-39 of IBC 2012. There is clarification of requirement for
automatic and manual standpipe. There has been confusion in past additions.
If you do not have IBC 2012 let me know.

Brad

-----Original Message-----
From: Matt Grise [mailto:[email protected]] 
Sent: Wednesday, January 23, 2013 2:45 PM
To: [email protected]
Subject: RE: manual vs automatic standpipes

Not sure what the reasoning is yet.

Matt Grisé PE*, LEED AP, NICET II  
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Wednesday, January 23, 2013 2:43 PM
To: [email protected]
Subject: RE: manual vs automatic standpipes

The city of Henderson, NV has ordinance that classifies mid-rise buildings
as high-rise for purposes of standpipe water supplies, but not sure if there
are any other such requirements out there.   What's the stated intent or
reasoning?


Steve Leyton




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Matt Grise
Sent: Wednesday, January 23, 2013 12:13 PM
To: [email protected]
Subject: manual vs automatic standpipes

I am looking at a project where the AHJ may potentially require an automatic
standpipe (fire pump) in a non high-rise building.(city water is adequate
for fire sprinkler system)

Is this fairly common/has anyone else come across it?

Matt Grisé PE*, LEED AP, NICET II  
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to