Could it be a programming problem ie.  The point is set as a momentary relay 
and not a latching relay?

Just my 2 cents.

Lorenzo Hillman
Coordinator, Fire & Safety Inspections
Leon County Schools\ Facilities 
Cell. 850-933-6843
Office. 850-617-1782
FX. 850-617-1790

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of John Drucker
Sent: Wednesday, February 20, 2013 7:03 AM
To: [email protected]; [email protected]
Subject: Re: Flow switch problem

Is there a BFP on system ? 
John Drucker - Mobile Email

----- Original Message -----
From: [email protected] 
<[email protected]>
To: Sprinkler -Forum <[email protected]>
Sent: Wed Feb 20 06:55:16 2013
Subject: Flow switch problem

We have a wet system that is having problems with the flow switch.  The flow 
switch would send a signal and then stop and then send another signal.  This 
would be happening intermittently.  We figured the flow switch diaphram was bad 
and then replaced the flow switch with the same results.  The main drain test 
is 60 psi with 50 psi residual.  The inspector's test was a globe valve that 
would flow water intermittantly; so we changed it to a ball valve.  It flows 
water continuously now with the same problem with the flow switch.  We checked 
the vane on the flow switch and the pipe is clean, so it's not hanging up at 
the riser.  Any suggestions?


 
Jay Stough
Tilley fire Equipment Co.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130220/d61c272e/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity to 
which it is addressed and may contain information that is privileged and 
confidential, nor is it, unless specifically stated, intended to be relied upon 
by any person or persons other than the individual or entity named above and no 
warranties or representations are made or intended to persons or entities not 
named above.  If the reader is not the intended recipient, you are hereby 
notified that any dissemination, distribution or copying of this communication 
is strictly prohibited.  If you have received this communication in error, 
please notify us immediately by telephone, return this message to the address 
above and delete all copies.  Thank you.

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130220/b4aee6f7/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to