Jay, I suggest you call Ames.  Have seen this issue where this backflow was 
installed several times back around the year 2000.  We called them and they 
sent us replacement checks for the assembly and it fixed the problem.

W B Gooding, III
Fire Sprinkler Division Manager
Dorvin D. Leis Co, Inc
c - 808-870-3294
f - 808-792-0429
o - 808-792-0416

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Jay Stough
Sent: Wednesday, February 20, 2013 3:25 AM
To: [email protected]
Subject: Flow switch problem

>From a drain valve w/ broken sprinkler.



Jay Stough


________________________________
 From: Justin Reid <[email protected]>
To: Jay Stough <[email protected]>; "[email protected]" 
<[email protected]>
Sent: Wednesday, February 20, 2013 8:06 AM
Subject: Re: Flow switch problem

Is the flowing water coming from a pressure relief valve? Or from the drain 
valve?

Justin Reid

Sent from my iPhone

On Feb 20, 2013, at 7:37 AM, Jay Stough <[email protected]> wrote:

> I'll try to answer all the ideas in one email.  The system does have an Ames 
> 2000SS backflow, but the water flow from the inspector's test is continuous, 
> so I don't think the backflow is preventing the water from flowing.  We 
> observed the lever and it is going up and down, not staying down.  The switch 
> is new out of the box, doing the same as the old.  We set the delay at the 
> middle setting.  If it is set too low, they get false alarms.  If they set it 
> up all the way, it does not give a signal for 2 minutes.  I will have the 
> guys check for air in the system since we are doing work there and taking the 
> system up and down every day.  It's an old scheduled system from the mid 
> 70's.  We've had systems with air in it, but have never had this type of 
> problem with a flow switch that replacing the globe valve didn't fix.
>
>
> 
> Jay Stough
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20130220/346d765d/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to